On the Refrigerated building I spoke of recently, I wonder if someone can check my math on the load. I have:

2- 3 phase scroll type compressors with
a RLA of 12.2 amps ( 12.2 X 2)= 24.4
25% of largest motor = 3.5

2 unit coolers inside:
The fans in each unit pulls:3 amps
( 3 X 2 )= 6.0

The defrost cycle for each pulls:
11.7 amps( 2 X 11.7 ) = 23.4

VPL ( I'm not sure what this is) = .8
Anti-sweat heater = 1.47
5 - 100 watt. lights = 4.17

Total load = 63.74

Anybody see that I'm missing something??
I'm presuming the fans run all the time
inside, according to what the rep. said,
even when they are in defrost cycle??
I thought they stopped during defrost,
myself, maybe I misunderstood him. Hope this comes out like I got it typed and not jumbled up...Thanks for the input.. Steve [Linked Image]
Posted By: mj Re: Load for feeder - 12/05/02 06:33 PM
check your 3. phase math calculations, i thank you total load will be about 15 amps less