ECN Forum
1. Assume a house has a ufer and the water and gas are done in plastic or the flexible gas pipe. Neither are metal, do we still have to bond them?

2. Protecting the main grounding electrode conductor with conduit, etc. pertains to what sizes of conductor?

Thanks,
Byron
If the interior piping is plastic how would you bond it?
the stubs under sinks are copper. But I really don't see any point in doing so...just asking.

Thanks
It is not really a code issue but I would still bond a steel sink to the EGC of the counter receptacles via the copper piping. I couldn't cite a code section tho. I have a stainless counter top and sink in my kitchen and it is bonded to the cooktop EGC (no neutral load) and receptacle EGCs.

If you have a disposal it is probably bonding a steel sink.

... but I am a bonding freak. The steel in my driveway is bonded.
Originally Posted by bwise121
1. Assume a house has a ufer and the water and gas are done in plastic or the flexible gas pipe. Neither are metal, do we still have to bond them?

Nope, how?

Quote
2. Protecting the main grounding electrode conductor with conduit, etc. pertains to what sizes of conductor?

All of them. 250.64
I believe that there are bonding requirements for the CSST? flexible gas lines. These may come from the piping manufacturer, not the NEC.

After looking found this.
http://www.toolbase.org/pdf/techinv/csst_lightningconcerns.pdf
I think Sparky's answer is oversimplified. It's never wrong to protect them with conduit as long as a steel conduit is choked on both ends, but 250.64 (B) certainly says that there are situations where a grounding electrode conductor size 6 or larger may not require conduit as a means to physically protect it. Guys?
When not subject to physical damage. A common issue I see in unprotected grounds is exposure to weed whacking and brushing around the ground wire.
© ECN Electrical Forums