Posted By: derater Receptacles above drop ceiling ? - 02/27/08 12:21 AM
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks
Posted By: JBD Re: Receptacles above drop ceiling ? - 02/27/08 01:35 AM
Originally Posted by derater
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks


Yes absolutely receptacles are allowed above drop ceilings.

However you may not use them to feed a flexible cord, because 400.8 does not allow flexible cords above ceilings.

Low voltage transformers (wall warts) may be plugged directly into the receptacle if they are Class 2 devices and their output cord is not one of the NEC prohibited flexible cord styles. another use for these receptacles would be for portable/temporary equipment (i.e. work light)that is removed prior to "closing" the ceiling.
Posted By: ghost307 Re: Receptacles above drop ceiling ? - 02/27/08 02:56 PM
As long as someone wants me to provide a receptacle above the ceiling for those purposes, I'm fine with it.
But as soon as they say that they want it to plug something into it and leave it (like a condensate return pump), I get antsy. I don't want to be part of their violation of 400.8; I wish that the Code was worded differently...it seems to be trying to fix one problem by addressing a different issue.