Posted By: Redsy 208/230 RTU----240 Supply - 01/29/08 03:12 AM
Rooftop Unit Nameplate Voltage 208/230 (3-phase), system voltage 240 (3-phase).
Reefer man says it's OK.
Which voltage (208, or 230) do you use to dedermine 10% tolarance level?
I know we've been her before, but what was the final verdict.

Deja Vu?

Posted By: renosteinke Re: 208/230 RTU----240 Supply - 01/29/08 03:50 AM
You use them both ...90% of 208 for the minimum, 10% of the 230 for the max.
Posted By: Redsy Re: 208/230 RTU----240 Supply - 01/30/08 03:02 AM
Thanks, Reno!

I was thinking the same thing, but I thought there was a previous link that discussed the issue.

John