I have just recently acquired my electrical contracting license here in AZ. My backround is new commercial construction. Every company I have worked for, had at
least one control guy who did the control work. I understand the basics, but my knowledge of available components for a particluar application is weak. Now that I am on my own, diving in seems to be the quickest way to accelerate the learning curve. I am hoping you guys will tolerate my ignorance
I looking for a relay with timer. It must be 120v control 120v 20 amp load. with timer sequence beginning after control power has been switched off, direct mount socket. It's gonna control a 1/4 horse E fan in a restaurant.
Thanks
Do you have a "Grainger" catolog? They offer tons of diferent control relays along with very good discriptions about their usage. Or go to
www.grainger.com Armed with their information, you can then decide which Manufacturer to use.
I like
this time delay relay as you can do almost any timing function that you can think of if you by the 11 pin version. The contacts are rated at 10A restive and 1/3hp 120/240 VAC.
Don
Another common brand is Omron relays. They have numerous types of sequences, ratings, times, etc.
I suspect most of the bigger supply shops carry them.
Grainger's multifunction Dayton relay has worked pretty well for me:
http://www.grainger.com/Grainger/items/6A855
Don that TRDU120A3 is a nice product but they want $65 for it.
Thank you all for the quick reply
Waterdog,
Just a quick note that you may have already realized. To accomplish what you want with most of the relays suggested you must have a constant 120V to the relay & you control the relay thru the switch terminals. So if you remove the 120V control power to the relay the output contacts will open up immediately. The only manufacturer that I know of that makes a relay that would be a time delay off relay w/o constant control power is an
Agastat timer. They are expensive but very reliable.
I have learned this info the hard way. Good luck.
Thanks AndyM, and you are correct, though pnuematic timers are available from many manufacturers Square D, Allen-Bradley, etc..
For those unfamiliar with them, they went out of style and are not commonly used anymore for general use mainly due to the far greater cost (list $300 and up versus under $100). They are also limited because of their mechanical nature to relatively short timing cycles and somewhat sloppy repeatablitiy typically around 10-15%.
AndyM, I am impressed with Agastat's wide range of timings available. I will have to keep that in reference somewhere in the back of my mind. They will work well for generator off delay timing where they will simplify the control circuitry for minimum run times and generator cooldown.
Shane
I work in the electric power industry & we use Agastats all the time. Most of these applications are on 125VDC control circuits. They are built well & last.
I have recently had a SCADA/control job where I learned the hard way the difference between these 2 types of time delay off relays.
Interesting to hear other fields don't use the pnuematic type much. Nice to learn what is happening outside my field.
Andy
I didn't chime in earlier because I didn't feel that the OP gave enough specific info. Was it to time delay on an actual loss of control power or a switching, things like that. Although I've dealt with a few of the expensive pneumatic bleed delay release Agastats, I've never designed around one. You shouldn't have to. The ladder that you're sensing loss of power on won't have power, but the circuit that you're controlling must. So just use a simple, cost effective, Time Delay Operate relay on your controlled circuit. Drive it with a NCHO (normally closed, held open) contact of a POK (Power OK) relay. If you want to switch back immediately, POK is just a standard control relay with its coil across the ladder. If you want to delay switching back, just use another TDO as the POK relay. A little thought on the design will let you buy a box of suitable relays for the price of that special Agastat.
Joe