Posted By: Don Hopkins Green Wire Green - 11/07/02 01:34 PM
At one time I thought the 'green wire' ground
in an appliance, computer, ETC. must use mechanical contact for 'bonding' i.e. soldering was not allowed. Is this true?
Thanks...

[This message has been edited by Don Hopkins (edited 11-08-2002).]
Posted By: Tom Re: Green Wire Green - 11/07/02 09:21 PM
Beats me. If you don't get a good reply here, you might want to try contacting UL & see what they have to say about it.

Tom
Posted By: therain4 Re: Green Wire Green - 11/07/02 09:56 PM
article 250.148 "connections depending solely on solder shall not be used
Posted By: resqcapt19 Re: Green Wire Green - 11/07/02 11:17 PM
The NEC does not apply to the internal wiring in computers and appliances.
Don