Posted By: Cinner DC System - Grounding and fusing! - 03/28/07 02:16 AM
Which is grounded in a DC system, the (+) or the (-)? Which is refereed to as the common? And finally which one is fused? I always thought or was tought that the neutrons flow from (-) to (+) therefore I was thinking that the (-) is the hot...but I am seeing differently in prints.
Posted By: gfretwell Re: DC System - Grounding and fusing! - 03/28/07 03:11 AM
These are all design issues. The TELCO grounds the + because they say it helps electrolysis problems. "Common" may be the ground but it is also used to identify a point where two or more supplies are connected together. Your PC supply is an example. There are several voltages, some connected + to common, the others - to common (AKA DC ground), which gets grounded to the case and EGC from the system board mounting tabs. The result is you have plus and minus voltages, referenced to ground.
Posted By: dereckbc Re: DC System - Grounding and fusing! - 03/28/07 06:28 PM
I can help with this as I have designed Telco plants for about 30 years.

It is completely a design issue. You can ground either polarity or none of them. As a general rule here are the standards.

-48 Volt DC plants bond the positive polarity to ground, referred to as return or common. The hot or negative polarities have the OCPD installed.

+12 and +24 Volt DC plants bond the negative polarity to ground, referred to as return or common. The hot or positive polarities have the OCPD installed.

The third option is to float the plant where neither polarity is grounded. In which case ground fault detection is installed and both polarities have OCPD installed. Very rare and very expensive to implement.
Posted By: Jonno Re: DC System - Grounding and fusing! - 03/28/07 08:16 PM
My experience is with bulk DC (typicaly 120V, 20A branch circuits, 100 and 150A rectifier output) for lab use. The supplies that we use are rectified off of the AC mains, and of course filtered.

In this case distribution is thorugh a DC listed pannel with two busses. Two pole CBs are used one protecting positive and one negative.

Ground fault portection is provided by the neutral bond at the rectifier. One of our rectifers has the ability to float this bond, but it has an integral GFCI.

This setup is used maily for power DC motors, and sometimes for the input stage of DC/DC converters, any application that requres 'clean' DC I still use a small switchmode suply.
Posted By: SteveFehr Re: DC System - Grounding and fusing! - 03/29/07 12:29 AM
The - side is usually "grounded" because it helps reduce galvanic corrision. Water molecules are polarized- because of wave physics and molecular geometry, the electron spends relatively more times around the oxygen atom than the hydrogen atoms. As a result, the oxygen atom has a slight - charge and the hydrogen molecules a slight + charge. So, if we give the steel chassis of a car (or a building, plane, ship, flashlight, etc), it repels the oxygen atoms in water and is less likely to oxidize and corrode. The + terminal, on the other hand, agressively oxidizes, but it's a relatively small area and can be maintained with dielectric grease or cleaned off.

Vehicles and other items that aren't solidly grounded (cars, etc) will always ground - and fuse +.

On our DC circuits (UPS batteries, 384 or 480VDC), we ground the - terminals and run the + through the breakers, but I think it's more habit than anything else- it's a benign environment and considering it's grounded, grounding the + would actually make more sense from a corrosion-prevention standpoint.
Posted By: JoeTestingEngr Re: DC System - Grounding and fusing! - 03/29/07 12:37 AM
Most of our DC sources are left floating. Of course our biggest source, traction power, has the negative return at a near ground potential. Since the return path is also part of the supporting structure of trucks wheels and running rails, it would be very hard and dangerous to elevate it well above ground. Since touching the third rail is as dangerous as messing with Social Security, it is kept elevated and isolated on stand-offs called frogs. If one of these frogs gets fried, it will not taste like chicken.
Joe
Posted By: Trumpy Re: DC System - Grounding and fusing! - 03/29/07 07:11 AM
This is rather interesting with all you US people saying that the Positive is always the Pole Grounded, here it would be the Negative,
people have been arguing about this since electricity was discovered, as in which way does the current flow?.
There is Conventional Current Flow(+ve to -ve) and there is Electron Current Flow (-ve to +ve), the US being (obviously) different to anything the English did, took on Conventional current flow ideas, that is why most cars in the US have a positive ground in them, while the rest of the world is negative ground.

Posted By: iwire Re: DC System - Grounding and fusing! - 03/29/07 08:25 AM
Originally Posted by Trumpy
that is why most cars in the US have a positive ground in them, while the rest of the world is negative ground.


Mike there has not been a 'positive ground' car made in the US since I would bet the 1940s or earlier.

I was under the impression that was an English practice. I believe Triumph Motorcycles where positive ground.
Posted By: pauluk Re: DC System - Grounding and fusing! - 03/29/07 11:39 AM
Quote
I was under the impression that was an English practice.


Indeed. Many British vehicles were positive-chassis right up until the 1960s.

Quote
This is rather interesting with all you US people saying that the Positive is always the Pole Grounded, here it would be the Negative,


Don't N.Z. telephone exchanges use positive ground on the batteries?

Quote
Of course our biggest source, traction power, has the negative return at a near ground potential.


As does the traction power for the 3rd-rail system employed on the southern region in Britain as well.

The London Underground (subway), however, actually uses a 4-rail system with neither pole solidly grounded. Balancing resistances are used to set the potentials in a 1/3 to 2/3 proportion, resulting in nominal voltages of about +420V and -210V relative to ground.

The outside conductor rail is the positive, central rail is the negative:

[Linked Image]

Posted By: SparksNmore Re: DC System - Grounding and fusing! - 03/29/07 12:39 PM
As for US built vehicles, as far as I know GM were always negative ground while Ford and Chrysler were positive ground until around 1955 when the transistor became popular and most cars went to 12 volt.
Posted By: Alan Belson Re: DC System - Grounding and fusing! - 03/29/07 07:25 PM
Our 1956 'Rover 60' two liter sidevalve had positive-earth electricals. I seem to remember some guys in my office saying that positive-grounding increased the rate at which the car body rusted?


Actually, we can thank Ben Franklin for this glorious way of confusing the ignorami. [ IMO People who fold paper shouldn't be playing with electricity anyway ].

Ben denoted +/- for direct currents decades before the likes of Ampere started electrocuting frogs in the name of science, but as he had no way of knowing which way the electrons flowed, he had to guess.


that true and what more many very old cars and some truck from that era did have 6 volts system that was pain in butt system they used the 6 volt until right after the mid to late 40's they went 12 volt expect the miltary trucks they always ran on 24 volt the same with miltary aircraft the DC system is 24 volt but on ac system it will be eiter 120 or 208 depending on set up

but just watch out in future i heard they are talking have a car run on 48 volt on basic system and have hybird drive system that actally run apx 110 -120 volt or so but i heard it can be high as 360 volts but i dont have the fact with me

Merci , Marc
Posted By: Texas_Ranger Re: DC System - Grounding and fusing! - 03/31/07 06:06 PM
Household DC systems once had a grounded center and ungrounded + and - like today's computer power supplies, giving 120/240V or 220/440V.
I once read about traction systems that have a grounded + rail and - overhead wire, but I can't remember any details.