#9989 05/29/02 05:39 AM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
that's worse... [Linked Image]

#9990 05/29/02 12:38 PM
Joined: Aug 2001
Posts: 7,520
P
Member
That reminds me of a photo I saw of a pole in some poor part of India where people regularly added their own unofficial drops to the lines.

At least this one looks as though they're being metered for it, but it sure leaves something to be desired. [Linked Image]

#9991 05/29/02 02:25 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
I believe that particular pole was found somewhere in the Caribbean. (Arc picture entry about halfway above revised with historical info/corporate memory.)

#9992 05/29/02 08:07 PM
Joined: Nov 2001
Posts: 280
M
Member
OMG, if someone doesnt pay their bill how do they know which one to red-tag ?

#9993 05/30/02 01:52 AM
Joined: May 2002
Posts: 68
H
Member
I went to Venezuela a long time ago and that was exactly what I saw and the customer did his own hookups right through any open window or hole in the wall.

but electric I thought I wasn't caculating it right as I was trying to figure the voltage drop then multiply divide it into the primary voltage. too late in the evening

[This message has been edited by hurk27 (edited 05-30-2002).]


Be Fair, Be Safe
Just don't be Fairly Safe
#9994 05/31/02 08:20 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Re the probable losses in transmission, I've sat down and re-read the whole Canterbury University article in detail.

They mentioned a 25A limit on an SWER feeder. Given that the highest quoted voltage is 19.1kV (one leg of a 33kV 3-ph system) that works out to a maximum loading of approx. 477kVA (they quote 500kVA, but who's arguing? [Linked Image]).

Given an overall ground resistance of 5 ohms that was quoted above, the loss would be 3125 watts, or less than 0.75% of the power being transmitted. Here are some quick figures for other ground resistance values:

10 ohms, 6.25kW, 1.3%
25 ohms, 15.6kW, 3.3%
50 ohms, 31.2kW, 6.5%
100 ohms, 62.5kW, 13.1%
250 ohms, 156kW, 32.7%

That's at full load, of course. At 25% loading (119.375kW, 6.25A) the figures are more reasonable even at high resistance values:

5 ohms, 195W, 0.16%
10 ohms, 391W, 0.33%
25 ohms, 977W, 0.82%
50 ohms, 1953W, 1.64%
100 ohms, 3.9kW, 3.3%
250 ohms, 9.8kW, 8.2%

#9995 05/31/02 10:33 AM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
An umetered loss, a loss to the poco...

#9996 05/31/02 12:11 PM
Joined: Aug 2001
Posts: 7,520
P
Member
True.... But I bet they allow for it in setting their rates, just as they would allow for losses on a Cu/Al line, in xfmrs, etc.

#9997 05/31/02 02:56 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
For a 3%-impedance pole transformer, the load loss is {surprise} ~3% at rated.

You bet utilities allow for distribution lossses in their rates.

Really though, without having a peer-reviewed paper on the matter, aren't we all taking pot shots at the real numbers?


[This message has been edited by Bjarney (edited 05-31-2002).]

#9998 05/31/02 05:31 PM
Joined: Aug 2001
Posts: 7,520
P
Member
You're probably right -- Some actual figures from SWER systems already in use would be good.

But however low that ground resistance, I still wouldn't wanna be near a rod that goes straight to a 19.1kV source through a xfmr.