disconnecting means for Shore receptacles for ships #99703
08/31/06 01:02 AM
08/31/06 01:02 AM
I
ih17dka8  Offline OP
Junior Member
Joined: Jan 2006
Posts: 8
Seoul, South Korea
Could push button connected to shunt trip coils be the disconnecting means for shore receptacles per NEC 555.17(B)? That's kind of remote contact to trip the circuit breaker for shore receptacles(500A).

------------------------------------------
NEC 555.17(B)Location. The disconnecting means shall be readily accessible, located not more than 762 mm (30 in.) from the receptacle it controls...

2017 / 2014 NEC & Related Books and Study Guides
Re: disconnecting means for Shore receptacles for ships #99704
08/31/06 12:11 PM
08/31/06 12:11 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
I believe the intent is that the user will be able to connect the shore tie cable without power being applied and then turn it on. How would you turn the shunt trip breaker back on ?


Greg Fretwell
Re: disconnecting means for Shore receptacles for ships #99705
08/31/06 01:36 PM
08/31/06 01:36 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
I just went to several sources for the recomended procedures for checking shore ties and they all concur that you must turn off the power at the shore post and the breakers in the boat before you plug in the cable. Then you turn on the shore power, verify the polarity indicators in the boat read OK then turn on the boat breakers.
You could not use a shunt trip for the post and follow this procedure without taking a long walk to a location you may not be aware of. That would encourage people to handle a hot cable in a wet environment. Bad idea.


Greg Fretwell
Re: disconnecting means for Shore receptacles for ships #99706
09/02/06 04:05 PM
09/02/06 04:05 PM
M
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
What about a motor operated breaker with a remote open/close selctor switch, and indicator lights and/or meters to verify zero volts? What type of connectors are you using at 500A? Cam Lock?

Motor operated is expensive, but it might be cheaper than an extra 600A disconnect.

Re: disconnecting means for Shore receptacles for ships #99707
09/03/06 02:21 PM
09/03/06 02:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
I agree that would meet the intent of the code.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,149
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,406 Are you busy
187,336 Re: Forum
176,674 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9693 MB (Peak: 1.1086 MB) Zlib enabled. Server Time: 2018-09-23 22:20:09 UTC