Please give an example of where a non-fusible service disconnect can be used.

Thank you

[This message has been edited by Frank Cinker (edited 08-30-2006).]

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Nov 2000
Posts: 2,148
R
Member
Frank,
The only way you can do that is if you put the OCPD immediately adjacent thereto. 230.91
Don


Don(resqcapt19)
Joined: Mar 2005
Posts: 399
A
Member
As a "utility company" disconnect ahead of a meter socket it must be rated for service duty. They do not have OCP and are not the "service disconnect".
They are frequently used where a standard pull out meter socket is used for 480 V 3 phase, corner grounded, 200 amp or less on sewer lift stations. After the meter is the "service disconnect".
Bonding and grounding confusion with this kind of installation is extensive.
Alan--


Alan--
If it was easy, anyone could do it.