ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 703 guests, and 46 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jul 2001
Posts: 311
F
Member
Please give an example of where a non-fusible service disconnect can be used.

Thank you

[This message has been edited by Frank Cinker (edited 08-30-2006).]

Horizontal Ad
Joined: Nov 2000
Posts: 2,148
R
Member
Frank,
The only way you can do that is if you put the OCPD immediately adjacent thereto. 230.91
Don


Don(resqcapt19)
Joined: Mar 2005
Posts: 399
A
Member
As a "utility company" disconnect ahead of a meter socket it must be rated for service duty. They do not have OCP and are not the "service disconnect".
They are frequently used where a standard pull out meter socket is used for 480 V 3 phase, corner grounded, 200 amp or less on sewer lift stations. After the meter is the "service disconnect".
Bonding and grounding confusion with this kind of installation is extensive.
Alan--


Alan--
If it was easy, anyone could do it.

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
558,663 Are you busy
432,946 Re: Forum
401,943 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5