Fire Alarm System Supply #99684
08/30/06 06:49 AM
08/30/06 06:49 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 609
massachusetts
The fire department wouldn't sign off on final inspection of low voltage fire alarm system in a new dwelling because the 120volt power supplying the transformer for the system was connected to a receptacle on a branch circuit feeding the garage lights.

He insisted that it must be connected to a circuit that feeds an area such as a bedroom.

I changed things so it was connected to a kitchen lighting circuit and he was OK with that.

He was concerned that if power went out to the garage lighting circuit that the owner may not realize it for some time...

This is in Massachusetts and the system is NOT hard wired 120 volt smoke detectors. This is a monitored (as long as they pay for the service) fire alarm system with battery backup.

Any comments to this and code references?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Fire Alarm System Supply #99685
08/30/06 02:24 PM
08/30/06 02:24 PM
J
John Crighton  Offline
Member
Joined: May 2005
Posts: 177
Southern California
Quote
He was concerned that if power went out to the garage lighting circuit that the owner may not realize it for some time...


They wouldn't notice the continuous beeping of the controller, complaining about the power failure?

I don't think you'll find any code reference on this one. It sounds like a pure judgement call by the AHJ.

Re: Fire Alarm System Supply #99686
08/30/06 05:01 PM
08/30/06 05:01 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I know that the post has to do with a residential issue but I think the inspector should rethink his call. Fire alarm systems unlike single station smoke alarms have a much better alerting system that you might think. If you have off site monitoring there is notification off site and on site. that not only goes for loss of A/C but also low battery plus other troubles. And if you take a lesson from the non-residential fire alarm installations, it will and should be on a dedicated circuit with nothing on it but the fire alarm system with a locking device on the breaker handle and no gfci or afci protection.


George Little
Re: Fire Alarm System Supply #99687
08/30/06 05:24 PM
08/30/06 05:24 PM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
Being this is in Mass.

There are no amendments to 527 CMR 12:00 that would require this, I am of the opinion that the State Building Code is silent regarding the source of energy for fire alarm systems (although I do not have one with me).

Multi station smokes are another issue in new construction they would most likely (residntial) require AFCI protection (bedrooms).

Charlie

[This message has been edited by cpal (edited 08-30-2006).]

Re: Fire Alarm System Supply #99688
08/30/06 10:16 PM
08/30/06 10:16 PM
M
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
I agree that this should be done as a commercial job: on its own circuit with a handle lock on device. I'm not sure which code requires this, but I've seen it, that would be a good question for the fire alarm group.

Out of curiosity, what brand/panel did you use for your install? I have a residential customer who's interested in a small addressable system, I'd like to see what others are installing.

Mike

Re: Fire Alarm System Supply #99689
08/30/06 11:30 PM
08/30/06 11:30 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Mike- it's NFPA 72 that ask for breaker lock and dedicated circuit.


George Little
Re: Fire Alarm System Supply #99690
09/01/06 11:14 AM
09/01/06 11:14 AM
E
Elec N Spec  Offline
Member
Joined: Jul 2006
Posts: 33
Rochester Hills, MI USA
George,

Don't you require smoke detectors in residential bedrooms to be on ark fault Breakers?

Re: Fire Alarm System Supply #99691
09/01/06 04:12 PM
09/01/06 04:12 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Quote
Don't you require smoke detectors in residential bedrooms to be on ark fault Breakers?


Smoke detectors and smoke alarms are two different items. "Smoke Alarms" typically of the single station 120v. variety require AFCI protection in bedrooms because they are a 120v. outlet. "Smoke Detectors" on the other hand are usually 12v. and part of a fire alarm system and do not require AFCI protection. Terminology is the difference.

[This message has been edited by George Little (edited 09-01-2006).]


George Little
Re: Fire Alarm System Supply #99692
09/01/06 05:23 PM
09/01/06 05:23 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
During remodelling and adding new bedrooms, are new smoke alarms tied into an existing circuit required to be upgraded to AFCI, or grandfathered in?

Re: Fire Alarm System Supply #99693
09/01/06 05:47 PM
09/01/06 05:47 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Steve- We heard from Jim Carpenter, CEO and Executive Director of IAEI, that extending a circuit does not mandate AFCI protection. He kinda squirmed when I brought this up from the floor at a Michigan Chapter meeting but that was his answer. He sits on that Code Panel so he should be in a position to answer that question.,


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,470 Are you busy
187,388 Re: Forum
176,728 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.060s Queries: 14 (0.008s) Memory: 1.0107 MB (Peak: 1.1863 MB) Zlib enabled. Server Time: 2018-09-26 06:50:26 UTC