Slaughter House/Meant packing Plant #99667
08/25/06 07:21 PM
08/25/06 07:21 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
Any reason a Slaughter House/ Meat packing plant can't be wired all in P.V.C. ?? (For washdown purposes mainly.

2017 / 2014 NEC & Related Books and Study Guides
Re: Slaughter House/Meant packing Plant #99668
08/26/06 10:16 AM
08/26/06 10:16 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
No reason at all, according to the NEC. Actually, this is a very wet, corrosive place, and PVC might be a good idea.

That said... make sure the USDA inspector agrees!

Re: Slaughter House/Meant packing Plant #99669
08/26/06 03:12 PM
08/26/06 03:12 PM
L
livetoride  Offline
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
The meat packing places I have done PVC is required. You also have to use clamps that hold the conduit off the wall. I use 2 hole PVC straps that suround the pipe, they hold the conduit 1/8" off the wall so the pipe does not trap crud aganst the wall. Rod http://www.plumbingsupply.com/pipeclamps.html edit to add link

[This message has been edited by livetoride (edited 08-26-2006).]

Re: Slaughter House/Meant packing Plant #99670
08/27/06 08:55 PM
08/27/06 08:55 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
Quote
they hold the conduit 1/8" off the wall


Keep in mind that you need a 1/4" space behind the conduit unless it's nonmetallic conduit mounted to concrete, masonry, tile, or a similar surface.

See 300.6(D)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,660 Are you busy
188,793 Re: Forum
178,511 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9601 MB (Peak: 1.0925 MB) Zlib enabled. Server Time: 2018-11-21 12:00:54 UTC