If you think the inspector is right or has an argument please give me a code reference i can not find any NEC reference that supports his statement. 210.4 (B) But that's assuming that the garbage disposer and laundry receptacle are both on the same yoke (same duplex receptacle).
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Shockme,
My situation is that i have used two separate duplex receptacles(separate yokes) for the GB and the DW.
The inspector says " anytime yo have multiwire circuits with shared neutral (regardless of being on the same yoke or not)you have to use tied breakers.
Edward
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
Nikko, ask him to show you where in the code. He won't be able to.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Until 2008
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Thank you for your replies.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
Nikko, I must have misunderstood (or misread) your situtation. I used to have a boss who would make us install double pole circuit breakers whenever we used multiwire branch circuits. Me and another guy used to argue about it with him until one day we just gave up trying to convince him that it didn't need to be done. He told us both that it was his liability insurance and not ours. Now I work for a guy who prefers that I do not use 3-wire branch circuits even though in the end it'll save a few bucks and perhaps 'that' money could be going into my pockets!
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
I believe this is what IWIRE refers to
210.4 Multiwire Branch Circuits. (A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment. [ROP 2–10] FPN: A 3-phase, 4-wire, wye-connected power system used to supply power to nonlinear loads may necessitate that the power system design allow for the possibility of high harmonic neutral-conductor currents. [ROP 2–11] (B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates. [ROP 2-10]
very interesting!!
Charlie
[This message has been edited by cpal (edited 08-20-2006).]
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
You nailed it Charlie.
As a big fan of multiwire branch circuits I do not support this change.
I am hoping that the MA amendments will remove this protection for the unqualified.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
Bob As you know there is still time to submit a concern through the comment stage the pre print and ROP are not written in stone.
I will have a better feel for the MAss Amendments some time in late September.
Charlie
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
At least it will allow handle-ties, and need not necessarily be a common-trip unit.