ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Nightmare Panels
 Nightmare Panels

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 35 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#9959 05/24/02 02:16 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
I'm an apprentice out of local 46 in seattle. I take pictures of electrical work here and there. I have a question regarding the two starter switches. Each are individually piped on the load and line side to two exaust fans in a parking garage. However, there is a nipple between the two fusable overload protection devices. Any ideas about what this nipple is for. Why are the two starter switches connected together. Any suggestions would be a great help. _thanks--Andrew.

Horizontal Ad
#9960 05/24/02 05:20 PM
Joined: Oct 2000
Posts: 4,138
Likes: 4
Member
Andrew,

A difficult Answer here. Do you know if there are any wires in the nipple? I see things all the time that seem to have no logical explanation, you might have to find the installer to figure it out. But there could be some common control wirimg. (?)

Bill

[This message has been edited by Bill Addiss (edited 05-24-2002).]


Bill
#9961 05/24/02 05:44 PM
Joined: May 2002
Posts: 2
C
Junior Member
If there are no wires in it, it could have been used for addtional support ....just " a stab in the dark"

#9962 05/24/02 08:35 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Control wiring going back to the same place, and piped along with the power from one switch?


Ron
#9963 05/25/02 01:12 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
Yes, I also have a picture with the starter switches open and I can see that all three phases on the load side of the fuse feed into block (factory wired). The other end of the block goes to feed the fan. while some low voltage colors go through the nipple into the other starter switch. I cant figure out why these two starter switches would need to control. Maybe they both must be on at the same time. So if one stops, so does the other. Well, I very much appreciate your suggestions. Thank you for your replys!-Erik

#9964 05/25/02 04:38 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Uhhmm, haven't you attacked them with your screwdriver yet? ;-) ;-) ;-)

I'd guess remote starting or remote status somewhere in the facility.

#9965 05/25/02 05:00 PM
Joined: May 2002
Posts: 1,716
R
Member
Don't know for sure, but it might have something to do with fire alarm shut downs.
Roger

Horizontal Ad
#9966 05/28/02 07:10 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Is the garage enclosed or open ? Is it possible that one fan is a fresh air supply and one is an exhaust? If so, there could be some sort of interlock to ensure that one is operating before the other starts.

#9967 05/28/02 10:27 AM
Joined: Oct 2000
Posts: 4,138
Likes: 4
Member
I was thinking it could be that the fans are on different circuits but use a common control power source.

Bill


Bill

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 7
Jam85 3
Popular Topics(Views)
329,178 Are you busy
254,113 Re: Forum
236,551 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5