Sizing Conductors for Voltage Drop-K value #99497
05/12/06 08:11 AM
05/12/06 08:11 AM
workn26  Offline OP
Junior Member
Joined: Dec 2005
Posts: 8
Here, I'm using the circular mills method as opposed to the resistive method:
To find the Voltage Drop of a single-phase ckt. I'd use: VD=2*R*L*I/CM
In order to size a conductor properly while staying within the 3% voltage drop recommendations I'd use: CM=2*K*L*I/VD
VD=voltage drop
L=length of conductor in ft.;one-way
CM=circular mills from Chap.9, Table 8
I=load current
R=the resistive value from Chap.9,Table 8 or 9
K=The D/C constant for the resistance of a 1000-mill conductor that's 1000 ft. long at 75 degrees C.

My question is with the K value. I've seen four different sets of values noted. The values are different for copper and aluminum.
The two sets that seem most accurate are:

An electrician on a different forum stated that he uses cu-7 & alu-11. I'm not too sure about that.
I've been using the first set thinking that keeping the value slightly higher is playing it safe.

Any takers on this one?

I'd appreciate it


2017 / 2014 NEC & Related Books and Study Guides
Re: Sizing Conductors for Voltage Drop-K value #99498
05/14/06 08:48 PM
05/14/06 08:48 PM
Yoopersup  Offline
Joined: Mar 2003
Posts: 840
K=12.9 Copper

K=21.2 Alum.

Both at 75'C

Single Phase Two wire
Vd= 2K X L X XI over CM
CM= 2KxLxI over VD

Is what I use

I got it out of Ugly's 2002 edition page (48)

Re: Sizing Conductors for Voltage Drop-K value #99499
05/14/06 08:56 PM
05/14/06 08:56 PM
workn26  Offline OP
Junior Member
Joined: Dec 2005
Posts: 8
Thanks a lot,

You know, I've got an Ugly's--I should've checked it out there.
Another helpful person, like yourself, gave me this answer:

The value of K is direcly determined by temerature. The resistance of a conductor is R = (K/A) x 1000 ohms/1000ft.
K = volume of resistivity in ohms-cmil/ft
A = cross sectional area in cmil

K = 10.371 at 20C for CU
K = 17.002 at 20C for AL
K = 10.575 at 25C for CU
K = 17.345 at 25C for AL
K = 12.9 at 75C for CU
K = 21.2 at 75C for AL




2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,860 Are you busy
181,981 Re: Forum
172,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9514 MB (Peak: 1.0749 MB) Zlib enabled. Server Time: 2018-03-23 04:57:46 UTC