Lighting is considered a continuous load. 210.19(A) and 210.20(A) limit continuous loads to 80% circuit capacity, so...
A 120-volt, 20-amp lighting circuit is limited to 1920 watts. A 277-volt, 20-amp lighting circuit is limited to 4432 watts. If you are using fluorescent or HID lighting don't forget to add ballast load.
Thanks Redsy! I tought there was a specific wattage ie(1380watts). My delema is that an architech has specified a single dimmer for two chandeliers with 900 watts each. So before I tell him his design is wrong and we need a dimming module or two seperate dimmers I want to cover my bases.