Supplemental Electrode Needed? #99309 03/13/05 09:35 PM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
If the metal frame of a building is bonded to the metal water pipe as allowed in 250.52(A)(2) method #2, then the metal frame is allowed to be the supplemental electrode as allowed by 250.53(D)(2)

With this scenario though, when the metal water pipe is replaced with plastic down the road, the electrode system is lost altogether.

We need to supplement this scenario with a additional electrode such as ground rods because the metal frame of the building will no longer be effectively grounded when the metal water pipe is replaced with non-metalic pipe.

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Supplemental Electrode Needed? #99310 04/01/05 02:02 PM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
250.52(A)(1) requires the metal underground water pipe to be in contact with the earth for 10 feet or more. As soon as you replace this pipe with non-metallic pipe, you have changed the grounding electrode system, and the GES must then be re-evaluated to meet current code. You don't get a free ride by going in through the back door.
This is why ALL work must have a permit applied for, so the inspector may determine if code compliance is achieved.


Earl
Re: Supplemental Electrode Needed? #99311 04/21/05 04:35 PM
Joined: Dec 2004
Posts: 1,064
D
Dnkldorf Offline
Member
earlydean, let's clarify your post.

250.52(A)(1) states that IF a metal water pipe IS to be used as a grounding electrode, it must be in contact with the earth for 10 feet or more.

250.52 doesn't state that a water pipe MUST be used as an grounding electrode.

EX. well water systems, plastic pipe incoming water.

However, if it is used as a grounding electrode and meets the earth contact requirement,it MUST be supplemented.

Does anyone else read it this way, or is it just me?

Dnk...

Re: Supplemental Electrode Needed? #99312 04/21/05 06:53 PM
Joined: Mar 2005
Posts: 3
C
clearyjr Offline
Junior Member
250.53(D)(2) Supplemental electrode required. Generally we look for 25 ohms or less of earth ground with one rod and water main, so if this is not achived then we install another rod etc.....
So metal water main or not 25ohms or better should be the rule.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,948 Are you busy
205,833 Re: Forum
193,912 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3