#99232 - 07/31/06 10:07 PM F/A  
sprkrob  Offline
Junior Member
Joined: Jul 2006
Posts: 5
etters,pa,usa
Today an inspector told me I cant put a flow and tamper switch on the same zone. My understanding is that they can be on same zone if they provide separate alarm and supervisory annunciation. This is a non addressable system. this is only thing on that zone and is programed waterflow/sup 1st floor. Am I correct???


2017 / 2014 NEC & Related Books and Study Guides

#99233 - 07/31/06 11:28 PM Re: F/A  
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 785
Chicago, Il.
How exactly were you planning to test for all those conditions on two wires of a non-addressable system?
Joe


#99234 - 08/01/06 06:50 PM Re: F/A  
energy7  Offline
Member
Joined: Jun 2002
Posts: 58
Oxnard, CA, USA
They have to be separate or addressible: The tamper is a "trouble" or "supervisory" signal; the water flow is an "alarm" signal.


#99235 - 08/01/06 09:38 PM Re: F/A  
sprkrob  Offline
Junior Member
Joined: Jul 2006
Posts: 5
etters,pa,usa
they are not separate but they do send different codes to central monitoring.
the zone is programed waterflow/supervisory.
flow switch sends alarm,tamper sends suprevision,trouble sends trouble.they are separate signals.there is also a separate ground fault LED. there is 2 resistors panel reads them.


#99236 - 08/04/06 11:01 AM Re: F/A  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
sprkrob
Help me out here guy. I've done a fair amount of fire alarm work and I'm at a complete loss as to how you get separate supervisory and alarm indications on a single zone with non addressable equipment.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#99237 - 08/04/06 11:19 AM Re: F/A  
rabbitgun  Offline
Member
Joined: Jul 2006
Posts: 23
I've done a bit of FA myself and have never seen this one either. Please post back with the name and model of the panel.


#99238 - 08/04/06 06:41 PM Re: F/A  
sprkrob  Offline
Junior Member
Joined: Jul 2006
Posts: 5
etters,pa,usa
OK
the panel reads 4.7K from EOL. You connect WF then 1.1k resistor then tamper then 3.6K then back through NEG. to panel. The panel reads the resistors. Pulls & smokes just have the 4.7 EOL on those zones. If the flow goes it reads 4.7 and goes to alarm. If tamper closes it reads 3.6 and supervision goes .You have to put 1.1 before tamper so panel can't read it. WF is NO, SS is NC. You program these zones to read it this way.


#99239 - 08/04/06 06:47 PM Re: F/A  
sprkrob  Offline
Junior Member
Joined: Jul 2006
Posts: 5
etters,pa,usa
OH,
Trouble and supervisory are 2 different signals when programmed this way.


#99240 - 08/04/06 08:30 PM Re: F/A  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 305
Maryland USA
All I'm going to say is : Thank the powers to be for Addressable systems !!
Beats the hell out of those old hard wired systems.


#99241 - 08/04/06 09:13 PM Re: F/A  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Sprkrob is correct, I have done this in the past also.

I have also just used the tamper (with no reduced resistor) to show an open circuit and activate a trouble/supervisory signal.

I think the inspector is wrong and just not familiar with the installation.

Roger

[This message has been edited by Roger (edited 08-04-2006).]


Page 1 of 2 1 2

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8158 MB (Peak: 0.9893 MB) Zlib enabled. Server Time: 2017-08-20 09:56:46 UTC