Residential Dining Rooms #99178
07/27/06 06:48 PM
07/27/06 06:48 PM
H
highground  Offline OP
Member
Joined: Nov 2004
Posts: 53
Chama, NM
Does the code require residential dining rooms to be served by a 20 Amp Circut?

Thanks in advance.

2017 / 2014 NEC & Related Books and Study Guides
Re: Residential Dining Rooms #99179
07/27/06 07:08 PM
07/27/06 07:08 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
210.52 (B) (1) seems to indicate that. This code could be worded better IMO. I have always wired dining rooms on a 20-amp branch circuit. I prefer the circuit to be separate from any of the small appliance kitchen countertop circuits though. And I always do a dedicated line for any refridgerator.

[This message has been edited by ShockMe77 (edited 07-27-2006).]

Re: Residential Dining Rooms #99180
07/27/06 09:17 PM
07/27/06 09:17 PM
T
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Depending on the size of the dining room and kitchen. I bring my 2 small appliance HRs into the dining room and work them over into the kitchen.


Shake n Bake
Re: Residential Dining Rooms #99181
07/27/06 09:36 PM
07/27/06 09:36 PM
M
mister h  Offline
Member
Joined: May 2006
Posts: 20
erie, pa. usa
Section 252(B)((1) states you need two circuits for the kitchen counter outlets. These circuits can feed dining room , breakfast rooms or simular areas, including refrigeration, ( I always put the refrigerator on it's own circuit) Remember the NEC states the minimum requirements. Note to 250.(B)(3) these circuits shall feed only one kitchen.

Ken


ken

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,583 Are you busy
188,735 Re: Forum
178,444 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9589 MB (Peak: 1.0922 MB) Zlib enabled. Server Time: 2018-11-19 01:14:49 UTC