#9913 05/20/02 08:51 PM
Joined: Nov 2000
Posts: 246
R
rmiell Offline OP
Member
How important is the rule for parallel conductors to be equal length?

Is there any leeway?

I am installing a set of 4 (phase A, B, C & Neutral) in a 4" PVC conduit, 6 times, for a 2000amp service.

How would you handle the length issue in this installation? Cut all the same length, based on the longest, and loop where needed?

What method is best to help train this wire? Has anyone used that new device that fits on a ratchet? I saw one at a trade show, looked like a good idea.

Any hints on how to do this?

Thanks in advance.

Rick Miell

#9914 05/20/02 10:33 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Rick,
The shorter the length of wire and the higher the load, the more critical the length becomes. I normally lay the conductors out and cut them all the same length before installing them. Finding space for the excess wire is sometimes a problem.
If you look at your installation and assume 4 sets of 600 kcmil with a calculated load of 1680 amps and multiple service disconnects and cable lengths of 20', 21', 22' and 23', we will find that the two shortest cables will be carryign more than there rated 75 degree ampacity. The 21' would be at 452, the 21' at 428, the 22' at 409 and the 23' at 391 amps. The rated ampacity of 600 kcmil is 420 amps.
Don(resqcapt19)


Don(resqcapt19)
#9915 05/20/02 10:39 PM
Joined: Dec 2001
Posts: 440
Likes: 3
Member
Rick,
It is important to get them close, but reality says that there will be some difference because all of the conduits don't enter the service equipment in the same place. I can't speak for the ratchet device. I've always used a hydraulic wire bender.
I used to have a problem from a class that I took that showed in theory how important it is to have the conductors the same length.
Good Luck, and let us know how the installation turns out.

Regards,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
#9916 11/10/03 01:01 PM
Joined: Jul 2002
Posts: 38
E
Member
I need to find out how inspectors are treating this rule that all conductors need to be the same length. Is there any standard percentage length difference that they allow?

I find that if there is a 10% difference in length between two conductors, there is approximately a 10% difference in the current through each conductor, with the shorter conductor carrying the larger portion of the current.

Also, do inspectors look at the whole installation as to how important it is for conductor length to be exactly the same.

For example, if you have 2 parallel - 1/0 conductors, 75C rated 150A feeding a 300A load. If there is any difference in length between the conductors, the shorter conductor would exceed it's ampacity rating.

But, if those same two conductors are feeding a 250A load, the ampacity of the shorter conductor is not exceed until it there is over a 30% difference in wire length.

Can anyone help me here?

Thanks,

Laura Jenkins
IBEW 48

#9917 11/10/03 01:29 PM
Joined: Oct 2003
Posts: 172
G
Member
for the length i have always worked that the shortest should be within 2%of the longest,

#9918 11/10/03 01:40 PM
Joined: Jul 2002
Posts: 38
E
Member
Are you basing that 2% off of anything in particular?

Laura

#9919 11/10/03 02:51 PM
Joined: Oct 2003
Posts: 172
G
Member
i am a canadian electrician and was taught this many moons ago,but if i have time i will look through the code book to see if i can locate this rule.