ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Nov 2001
Posts: 75
B
Bill39 Offline OP
Member
Please comment on the advice I gave to my friend about a problem he ran into this weekend and let me know if it was correct or if there was another alternative.

My friend and his brother traded home clothes dryers (don’t ask why) but now there was a 220V plug configuration problem. NOTE: this is in the USA.

My friend now has a 3-wire outlet and a dryer with a 4-wire male plug.
The brother now has a 4-wire outlet and a dryer with a 3 wire male plug.

He wanted to just put a 4-wire cord on the 3-wire dryer and a 3-wire cord on the 4-wire dryer (tying the ground and neutral together).

My advice was that my friend needed to install at his house a 4-wire outlet and run 4-wire Romex to it.
My advice to fix the problem at his brother’s house was to replace the existing 4-wire outlet with a 3-wire outlet connecting the ground and leaving the neutral wire disconnected at the outlet.

Right/Wrong/Alternatives?????

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2005
Posts: 214
E
Member
"My advice to fix the problem at his brother’s house was to replace the existing 4-wire outlet with a 3-wire outlet connecting the ground and leaving the neutral wire disconnected at the outlet."
If you were to do this it would result in current on the ground wire which is definetley not code legal. if he already has a four-wire plug just replace the cord, it's reletively cheap and inexpensive. Just open the back of the drier up, remove the N/G bond, hook ground/ground Neutral/Neutral and you have a code compliant installation.

-Will

(edited for spelling)

[This message has been edited by Elviscat (edited 06-21-2006).]

Joined: May 2002
Posts: 1,716
R
Member
They just needed to swap the cords when they traded.

Roger

Joined: Nov 2001
Posts: 75
B
Bill39 Offline OP
Member
I thought the 3rd wire on a 220VAC dryer outlet was a "ground" not a "neutral"?

So you're saying it is OK to tie the neutral and ground together inside the dryer?

Isn't there a good reason a 4th wire is on the newer dryers and would therefore need a 4-wire outlet?

I completely understand the difference between ground wire and a (grounded) neutral and that a true ground wire should not carry any current unless there is a fault.

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
OK, here goes. Bill, you probably already know this, but there are some reading this board that do not, so I will be overly simple for their benefit.

In the "old days" dryers and ranges had two "hot" wires, and a third that served both as a ground, and as a 'neutral' for incidental 120v. loads (light, timer, etc.) On these machines, there was a strap that connected the case of the appliance to the third wire.

For a variety of reasons (too involved to get into here), we separate the "ground" from the "neutral" back at the main panel. Simply put, the neutral wire is intended to always be carrying current, and to become "hot" if it comes loose.... while the ground is never intended, under normal circumstances, to be carrying current. It's just there, in case something bad happens.

So, dryers and ranges now get plugs with four prongs, and, in the case of romex, are hooked up to four wires. These units DO NOT have the case connected to the "neutral."

The correct solutions are:
1) The guy with the four-wire plug gets to run a four-wire cable to his outlet, and replace the receptacle; and,

2) The guy with the three-wire plug gets to replace it with a four wire cord..AND remove that 'bonding' strap in the back of the appliance.

This is one situation where it will 'work' even if it's NOT OK.

Joined: May 2002
Posts: 1,716
R
Member
Bill, there is no reason to change a three wire circuit to a four wire if the three wire circuit was compliant when the house was built, and assuming this is the case is the reason they just needed to swap cords with each other.

Just because you might have an older house and buy a new appliance doesn't mean you would have to rewire the house. Note the Exception to 250.140

Quote
250.140 Frames of Ranges and Clothes Dryers
Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be grounded in the manner specified by 250.134 or 250.138.

Exception: For existing branch circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be grounded to the grounded circuit conductor if all the following conditions are met.

(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.

(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.

(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.

(4) Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.

Roger




[This message has been edited by Roger (edited 06-21-2006).]

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Roger, my concern over replacing the four-prong plug with a three-prong type is that the case bond must also be replaced; it was likely removed when the cord was attached. I'd hate to see the case become ungrounded.

Joined: May 2002
Posts: 1,716
R
Member
John, I can see your concern but, whoever would change the cords should know what they are doing, especially if they were knowledgeable enough to be considering installing a new circuit.

If they hired an electrician to do this work, the electrician should tell them their options before installing and charging for a new circuit IMO.

Roger

Joined: May 2006
Posts: 20
M
Member
Don,t forget about the UL listing of the appliance.


ken
Joined: May 2006
Posts: 20
M
Member
And remember the old saying "it worked fine at the other house."

Have to watch the the liability.


ken