Are the inspectors allowing 3" pancake boxes for mounting light fixtures? Remember the cu. in. fill for this size box is 4 cu. in.
George Little
|
|
|
|
|
Joined: Jan 2005
Posts: 5,476 Likes: 3
Cat Servant Member
|
Sure- and why not?
Indeed, they are often used for ceiling fans as well.
The only problem is wire fill... if the circuit continues on to another fixture, then wire fill is violated. There's only enough room (legally) for one set of wires.
|
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
Short answer NO 4 cu inches ( 65 cm cubed) allows for the end of a 14 / 2, no ground, nothing else. Fixture canopys add space but, unless they are marked with the Cu. In. they should not be counted. Almost anyplace that a pan box can be used an L shaped box, i.e. pan with a wiring compartment on one side, would do better. I once asked an engineer at Raco why they kept making the 3" pans and he said, Because inspectors kept allowing them to pass inspection. ![[Linked Image]](https://www.electrical-contractor.net/ubb/frown.gif) Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
|
Joined: Mar 2004
Posts: 829
Member
|
reno you must be thinking he said 4" pancake like I did at first.
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Use listed #18 lighting whips in 3/8" Flex.
Problem gone....
You will need to have a junction box within 6 feet for the listed whip.
Alternately, for lighting only you can use the tap rules to run your own #18 even longer.
Look at NEC 2005 table 240.5
[This message has been edited by Tesla (edited 06-09-2006).]
[This message has been edited by Tesla (edited 06-18-2006).]
Tesla
|
|
|
|
|
Joined: Jan 2005
Posts: 5,476 Likes: 3
Cat Servant Member
|
Big B, I bet you're right. I'm not sure I've ever seen the smaller one!
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I let people use them if there is only one 14-2 in the box.
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Jul 2004
Posts: 10,029 Likes: 37
Member
|
Doesn't the fixture canopy add to the capacity? 410.10 Space for Conductors. Canopies and outlet boxes taken together shall provide adequate space so that luminaire (fixture) conductors and their connecting devices can be properly installed. If the luminaire had a flat base that effectively stopped the box fill at the face of the box I could see the concern but if this is a bell canopy there should be plenty of room, even for two sets of #12s.
Greg Fretwell
|
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
410.10 makes no mention of using the canopy of a fixture as space for branch circuit conductors, only the fixture conductors and their connecting devices. The branch circuit conductors are poperly housed in the box. If it were a 4" pan box it would properly house a single 14/2 WG NM cable and the fixture wires could be housed in the canopy. A 3" pan box is quite clearly not suitable for 14/2 WG NM cable but most of us, like Ryan would accept it.