Bonding per 680.26(C) #98754
06/04/06 07:02 PM
06/04/06 07:02 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Are the lugs and screws that are installed on pool & spa equipment by the factory suitable for bonding the equipment to the bonding grid? Do inspectors ask that the contractors replace these lugs and screws with ones made of stainless steel, brass or copper or other non-corrosive material?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Bonding per 680.26(C) #98755
06/04/06 08:39 PM
06/04/06 08:39 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Yes, and they shouldn't.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Bonding per 680.26(C) #98756
06/05/06 05:20 PM
06/05/06 05:20 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,041
Brick, NJ USA
George:
I have to agree with Larry
Yes, and why are they requested/required to be replaced??

John


John
Re: Bonding per 680.26(C) #98757
06/05/06 08:15 PM
06/05/06 08:15 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
John & Larry- I agree with you guys and so does UL. Once you start altering a UL Listed equipment you are inviting problems. The equipment is Listed with the lugs on it and that's where we connect the Bond wire. But, we still have some inspectors out there that read the wording about brass, copper or stainless connections and they have the contractors changing them. I say they are wrong for doing so.


George Little
Re: Bonding per 680.26(C) #98758
06/06/06 05:09 PM
06/06/06 05:09 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,041
Brick, NJ USA
George:
Perhaps it's time for a little CE or Seminar on Article 680??

Only mention of the SS, Brass of Cu lugs that I'm aware of regards bonding IG???

Maybe I missed something??

John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,903
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,641 Are you busy
188,776 Re: Forum
178,495 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9680 MB (Peak: 1.1074 MB) Zlib enabled. Server Time: 2018-11-20 21:46:14 UTC