408.4 2005 NEC #98703 02/19/05 08:05 AM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
How are we to apply the new language to circuit directory's for panels?

Better yet...how are inspectors going to enforce the new language of 408.4???

For instance I mark some of my branch circuits in panels as Bedroom, Bedroom, Bedroom/smoke detectors, kitchen counter plugs, kitchen counter plugs, etc

Am I now going to have to "include sufficeint detail" and label like this...

Northwest bedroom plugs, Southwest bedroom plugs and lights in da closets of the Northwest and Southwest bedrooms, Kitchen counter plugs near the sink, Kitchen counter plugs by the refridgerator and the one over by the wall oven too,etc...

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: 408.4 2005 NEC #98704 02/19/05 08:11 AM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
I think that is the point for the new wording of the article. I always marked that way anyway. What good are three or four circuits marked "Bedroom"? It makes sense that if you are going to lable that you actually label with enough info to make some sense out of it.

Re: 408.4 2005 NEC #98705 02/19/05 09:01 AM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline OP
Member
Most residential loadcenters only provide a small 1" x 1" labeling area next to the breaker to identify its purpose...which makes it difficult for sufficeint detailed labeling of branch circuits that feed multiple areas.

Do any of you actually type up a seperate directory?

shortcircuit

Re: 408.4 2005 NEC #98706 02/19/05 09:13 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Shortcircuit I turn a panel schedule into the office and they make custom panel labels with our company name etc.

That aside I have no idea how we will comply.

We wire large office spaces we will have many circuits that feed office cubicles.

How can I describe them?

East West runs out quickly with so many circuits. In the past we have posted the power prints in the electric room for reference.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 408.4 2005 NEC #98707 02/19/05 12:44 PM
Joined: Jan 2002
Posts: 163
D
dana1028 Offline
Member
As an inspector, what I often see in the field is breaker after breaker marked only 'receptacle' or 'lighting' with no indication as to where the receptacle or lighting circuit is.

I think the intent here is to give some sort of indication as to where the receptacle or lighting circuit is: bedroom rec., kitch. rec., dining....etc. would be much improved.

Re: 408.4 2005 NEC #98708 02/20/05 06:45 PM
Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
Ok so we want to improve the system, so we ask for all the connected equipment and outlets to be posted at the directory, so now the homeowner runs to the panel in a panic, finds a schedule with a confusing short story of every outlet and piece of equipment on a circuit, with, north, south east, west locations, at this point, the panic increases, as they try to understand what turns what off.
How about a flow chart posted at the panel.

Re: 408.4 2005 NEC #98709 02/20/05 07:49 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I think in commercial applications this will be relatively easy, like Bob, I always see typed, company specific panel schedules.

In residential I just see the panel schedule filled in with pen, but then again, given the number of circuits I don't think residential should be a problem either.

The one problem I do see, however: Small appliance branch circuits in a dwelling.


Ryan Jackson,
Salt Lake City

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 17
Popular Topics(Views)
272,150 Are you busy
206,031 Re: Forum
194,053 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3