I
iwire Offline OP
Moderator
Quote
410.110 Listing of Decorative Lighting.

Decorative lighting and similar accessories used for holiday lighting and similar purposes, in accordance with 590.3(B) shall be listed.


Quote
590.5 Listing of Decorative Lighting.

Decorative lighting used for holiday lighting and similar purposes, in accordance with 590.3(B) shall be listed.


I do not understand this, is the NEC now saying the AHJ for each area should require permits and inspections for end use equipment that is made to be plugged in to ensure compliance with the listing requirements?

I was under the assumption that the NEC stopped at the receptacle.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2000
Posts: 2,148
R
Member
Bob,
Quote
I was under the assumption that the NEC stopped at the receptacle.
A lot of the Article 422 requirements extend beyond the fixed wiring of the building. I once submitted a proposal to delete 422 because it is not within the scope of the NEC.
Quote
This Code covers the installation of electric ..
In my opinion most cord and plug connected equipment is not "installed".
Don


Don(resqcapt19)
Joined: Apr 2004
Posts: 201
Member
CMP-10 is taking the stance that the Code doesn't jump out of the wall to protect things that are plugged into the building wiring. That is what happened to 240.5(B)(1) and 240.5(B)(3) in the 2005 Code. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Joined: Aug 2003
Posts: 1,374
R
Moderator
I agree with you guys. I think this should be a NEMA or NRTL issue, not an NEC issue. Another example is the requirement to have inherent GFCI protection for vending machines.