Conduit for Pole Lights #9814
05/14/02 07:05 PM
05/14/02 07:05 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
When you set pole lights with concrete pedastals, how do you lay the conduit to make this job as easy as possible??

Assume pvc pipe in and out.

I went through another major thrash today because I screwed up. I wasn't on site the day the conduit was buried.....and that was about 9 months ago. We had problems finding all the conduits today and in fact didn't find them all. I think that I know how I'm going to do it in the future, but I'm looking for tips from you pros.

GJ

Work Gear for Electricians and the Trades
Re: Conduit for Pole Lights #9815
05/14/02 07:31 PM
05/14/02 07:31 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
GJ,
A template of the light can be made out of plywood (stack 5-6 pieces & drill 'em) to position the pvc before the pour...

Re: Conduit for Pole Lights #9816
05/14/02 10:19 PM
05/14/02 10:19 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
Sparky,
Yea, got that part down, the templates are not a problem.

How do you handle the conduit? Shallow trench? Do you ramp each conduit to the surface at the post?

I'm tired of standing on my head in an 18" diameter hole while I try to glue on a sweep. There's gotta be a better way.

GJ

Re: Conduit for Pole Lights #9817
05/16/02 01:58 AM
05/16/02 01:58 AM
H
hurk27  Offline
Member
Joined: May 2002
Posts: 68
Portage, Indiana
we just run the PVC to the pole with a 90 glued on before its set down in the trench so its centered on the hole for the sona tube with enough stub sticking up to be above the finished concrete also if you cant put on the 90 yet and have to bury the pipe temporarily throw in a tracing wire to be able to find it with a underground tracer like they do with sewer pipe


Be Fair, Be Safe
Just don't be Fairly Safe
Re: Conduit for Pole Lights #9818
05/17/02 06:33 PM
05/17/02 06:33 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
Hi Hurk, welcome to the board!

So if you install your sweeps and drop them in the trench, how do you auger out the holes later???? Isn't the conduit in the way?

GJ

Re: Conduit for Pole Lights #9819
05/18/02 02:41 PM
05/18/02 02:41 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
GJ,

What I have done [maybe 1000x's [Linked Image]] is to get the PVC 90 and the PVC which runs to / from the next pole base at least 12" below the bottom of the base. I'll jump in the base's hole [prior to the "Sonotube" being installed, or any of the metal] and make up the pole stub[s].

After the glue is dry, I'll backfill everything to eliminate movement and leaking Concrete [Linked Image]. If the Inspection is still pending, this gets done after Lure Inspecture gives the A-OK!.

We always set the Steel [REBAR cage], and when doing this, insert the previously mentioned Plywood template - which secures the bolt / stud pattern and the conduit stub[s]. I usually leave a good couple of feet sticking out above the top of the base, then trim it down when setting the light standards [poles] if needed.

Hope this is in the direction you are looking!

Scott S.E.T.


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Conduit for Pole Lights #9820
05/18/02 11:05 PM
05/18/02 11:05 PM
M
menegt  Offline
Member
Joined: Jan 2002
Posts: 34
sacramento, ca
Scott, do you throw in a 4' piece of sono
tube? or do you only use sono tube if you're going to have a two foot base above ground? if so, do you puncture the sonotube on the side to put your pvc? Also, have you ever tried using a compass to orientate your bolts?

Re: Conduit for Pole Lights #9821
05/19/02 12:38 AM
05/19/02 12:38 AM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
Scott35 said;
"is to get the PVC 90 and the PVC which runs to / from the next pole baseat least 12" below the bottom of the base. I'll jump in the base's hole [prior to the "Sonotube" being installed, or any of the metal] and make up the pole stub[s]."

OK, the bases I just did were 24"x6' deep. I don't think that will work for this situation. The bollards were 18"x3', too small to stand in, just barely able to work in by standing on my head in the hole!!

I'm really just looking for suggestions on what works for others, and I appreciate the comments so far.

What I plan to do in the future is to trench the conduit no deeper than 3' and slope the conduit to the surface at each pedastal. I'll cut and tape the pipe there and stake it so that i can find it again later.

If anyone has a better way, I'm interested.

GJ


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,297 Are you busy
187,231 Re: Forum
176,594 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9937 MB (Peak: 1.1524 MB) Zlib enabled. Server Time: 2018-09-20 04:50:34 UTC