Receptacles in Kitchen #98026
04/26/06 08:25 PM
04/26/06 08:25 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Contractor asked me if he could install receptacles underneath the upper cabinets in his/her kitchen that would be used for plugging in fluorescent slim line light fixtures. These receptacles would be in addition to the wall receptacles installed to serve the countertop. This subject has to have been on this BB before and I missed it. I have not seen the fixtures yet but have some concerns about them coming with the cord installed. Then there is the issue of GFCI protection? Plugs installed to serve the countertop will have GFCI protection.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Receptacles in Kitchen #98027
04/26/06 09:13 PM
04/26/06 09:13 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Good issues, George.

Assuming that the receptacles are more than 20" above the countertop, I don't think GFI protection is required. Under 20", and I think they would be considered as countertop serving receptacles, even if there are others.

Re: Receptacles in Kitchen #98028
04/26/06 09:21 PM
04/26/06 09:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
Are they 20" or less from the counter surface? Then they are clearly serving the countertop. Higher than that they are still SA circuits but would not have to be GFCI.
I am still not sure why they wouldn't/shouldn't be.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,573 Are you busy
186,303 Re: Forum
175,759 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9515 MB (Peak: 1.0759 MB) Zlib enabled. Server Time: 2018-08-17 13:04:38 UTC