#98026 - 04/26/06 08:25 PM Receptacles in Kitchen  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Contractor asked me if he could install receptacles underneath the upper cabinets in his/her kitchen that would be used for plugging in fluorescent slim line light fixtures. These receptacles would be in addition to the wall receptacles installed to serve the countertop. This subject has to have been on this BB before and I missed it. I have not seen the fixtures yet but have some concerns about them coming with the cord installed. Then there is the issue of GFCI protection? Plugs installed to serve the countertop will have GFCI protection.


George Little

2017 / 2014 NEC & Related Books and Study Guides

#98027 - 04/26/06 09:13 PM Re: Receptacles in Kitchen  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Good issues, George.

Assuming that the receptacles are more than 20" above the countertop, I don't think GFI protection is required. Under 20", and I think they would be considered as countertop serving receptacles, even if there are others.


#98028 - 04/26/06 09:21 PM Re: Receptacles in Kitchen  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Are they 20" or less from the counter surface? Then they are clearly serving the countertop. Higher than that they are still SA circuits but would not have to be GFCI.
I am still not sure why they wouldn't/shouldn't be.


Greg Fretwell


Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7528 MB (Peak: 0.8753 MB) Zlib enabled. Server Time: 2017-10-20 10:40:52 UTC