#97963 - 04/21/06 04:56 PM 210.70(A)(3)  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Multi-family dwelling unit. Basement storage with 11- 40 sq ft apx. separate storage sections.

Is a separate light and switch required in each section or is external lighting in the common basement area good enough?


2017 / 2014 NEC & Related Books and Study Guides

#97964 - 04/21/06 09:17 PM Re: 210.70(A)(3)  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
At the risk of being a smart A** I'd say what ever is called out on the plan is what I would look for on inspection. I don't know of any really specific minimum in the NEC. Common sense should prevail but we can only enforce code.


George Little

#97965 - 04/27/06 09:00 AM Re: 210.70(A)(3)  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
George,

I'm doing the plan review.


#97966 - 04/27/06 11:46 AM Re: 210.70(A)(3)  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
I think you may actually get more help from your building/safety code. You still need adequate illumination for egress don't you?
The NEC really only requires one light.


Greg Fretwell

#97967 - 04/27/06 02:36 PM Re: 210.70(A)(3)  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Common areas must be illuminated by a "house panel" branch circuit, if illumination is needed for any common area. If the engineer is trying to eliminate the house panel by providing for 11 separate luminaires to 11 separate storage areas, then I would fail the plans, unless enough light is shed on the common areas from another common area light fed from the "house panel".
Once the common area is illuminated (to 1 footcandle), then each storage area could be lit by it's own luminaire or lampholder, or by additional common area luminaires.
If the question is whether any lighting is required at all for the storage areas, the answer is no, so long as there is sufficient light shed from the common areas, to 1 footcandle.


Earl

#97968 - 04/27/06 05:59 PM Re: 210.70(A)(3)  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Steve- I didn't realize you were doing the plan review. I thought you were installing. That said ( grovel, grovel) I think earlydean as the correct approach.


George Little

#97969 - 05/01/06 08:17 PM Re: 210.70(A)(3)  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
George,
I only take the technical stuff you guys say seriously. [Linked Image]

The plans show lighting in the general area only (leading to the storage areas). I think there will probably be enough light, but I wanted to check and see what the board thought about the interpretation of this section. Thanks.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7842 MB (Peak: 0.9375 MB) Zlib enabled. Server Time: 2017-12-12 12:13:13 UTC