Multi-family dwelling unit. Basement storage with 11- 40 sq ft apx. separate storage sections.

Is a separate light and switch required in each section or is external lighting in the common basement area good enough?

Horizontal Ad
#97964 04/21/06 10:17 PM
Joined: Jan 2004
Posts: 1,507
G
Member
At the risk of being a smart A** I'd say what ever is called out on the plan is what I would look for on inspection. I don't know of any really specific minimum in the NEC. Common sense should prevail but we can only enforce code.


George Little
#97965 04/27/06 10:00 AM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
George,

I'm doing the plan review.

#97966 04/27/06 12:46 PM
Joined: Jul 2004
Posts: 10,010
Likes: 37
G
Member
I think you may actually get more help from your building/safety code. You still need adequate illumination for egress don't you?
The NEC really only requires one light.


Greg Fretwell
#97967 04/27/06 03:36 PM
Joined: Dec 2003
Posts: 751
E
Member
Common areas must be illuminated by a "house panel" branch circuit, if illumination is needed for any common area. If the engineer is trying to eliminate the house panel by providing for 11 separate luminaires to 11 separate storage areas, then I would fail the plans, unless enough light is shed on the common areas from another common area light fed from the "house panel".
Once the common area is illuminated (to 1 footcandle), then each storage area could be lit by it's own luminaire or lampholder, or by additional common area luminaires.
If the question is whether any lighting is required at all for the storage areas, the answer is no, so long as there is sufficient light shed from the common areas, to 1 footcandle.


Earl
#97968 04/27/06 06:59 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Steve- I didn't realize you were doing the plan review. I thought you were installing. That said ( grovel, grovel) I think earlydean as the correct approach.


George Little
#97969 05/01/06 09:17 PM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
George,
I only take the technical stuff you guys say seriously. [Linked Image]

The plans show lighting in the general area only (leading to the storage areas). I think there will probably be enough light, but I wanted to check and see what the board thought about the interpretation of this section. Thanks.

Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Top Posters(30 Days)
Popular Topics(Views)
363,487 Are you busy
286,303 Re: Forum
264,840 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5