ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
I have a walk-in freezer/refer with a fan coil hung from the ceiling in the freezer side. The freezer/refer is a prefab modular unit. You have to walk thru the refer to get to the freezer. They want a defrost
clock and fused disconnect in the electrical room about 5 feet away on the outside of the freezer. There are 5 conductors going to the 240V fan coil to control the defrost elements and fan motors from the clock. What
are the options for providing a disconnect for the fan coil? Do I need a 5 pole disconnect in the freezer?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2003
Posts: 4,391
I
Moderator
We usually use two separate disconect switches.

One for the fan power and the other for the defrost power.

Most times these are low current applications (under 30 amps) so we just use 1, 2 or 3 pole toggle switches in weather proof boxes.

No need for fused disconnects inside the chest.

[This message has been edited by iwire (edited 04-14-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jan 2004
Posts: 1,507
G
Member
In some situations these evaporator units have a cord/cap type hook up inside the unit that should be acceptable as as disconnect. IMHO. Of course you'd still need a disconnect within sight of the controller what and where ever it might be located.


George Little
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
I was thinking it had to be one simulatious
disconnecting means. two switches solves the problem. I have seen weatherproof boxes full
of condensation inside walk-ins. Is there any reason not to use conventional 4S boxes?

Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
I was thinking it had to be one simulatious disconnecting means.

As long as the switches are 'grouped' it is no problem.

Quote
I have seen weatherproof boxes full
of condensation inside walk-ins.

[Linked Image]

Yes that is a common problem and it is caused by failing to comply with 300.7(A)

Quote
300.7 Raceways Exposed to Different Temperatures.

(A) Sealing. Where portions of a cable raceway or sleeve are known to be subjected to different temperatures and where condensation is known to be a problem, as in cold storage areas of buildings or where passing from the interior to the exterior of a building, the raceway or sleeve shall be filled with an approved material to prevent the circulation of warm air to a colder section of the raceway or sleeve. An explosionproof seal shall not be required for this purpose.

If 300.7 is ignored you will get water.

Quote
Is there any reason not to use conventional 4S boxes?

No not really.

For my work it is usually a customer requirement.

But it is not a problem if you follow 300.7 and make a small drain hole in the box all is good.

Just trimming a notch in the covers gasket at the bottom is enough to make sure the box does not fill with water.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks. You guys are great. I appreciate the input.