#97897 04/13/06 10:03 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Hey Greg- I just checked the UL White Book and it says RNMC is not Listed for boat lift covers and you'll need "Special Permission" signed by at least 5 inspectors and you and I know that those 5 inspectors will need some "encouragement" and a boat ride before they sign off on "special permission" [Linked Image]


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#97898 04/14/06 12:50 AM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I have already taken 3 inspectors for that boat ride and provided some 12 oz ecouragement but if you think we need one more come on down.


Greg Fretwell
#97899 04/14/06 03:52 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Greg - 300.6 exception doesn't mention wood. The 2x4s between triangles is what I would be strapping to. Back to you.(pin-pong anyone?)

#97900 04/14/06 09:51 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
It is clear the wood is what you should be worried about. If it is treated it shouldn't rot. The RNC will be fine.


Greg Fretwell
#97901 04/14/06 11:55 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
You really need to back up and read the scope of 300.6 before we start nitpicking the language. Lets start over.
Quote
300.6 Protection Against Corrosion.
Metal raceways, cable trays, cablebus, auxiliary gutters, cable armor, boxes, cable sheathing, cabinets, elbows, couplings, fittings, supports, and support hardware shall be of materials suitable for the environment in which they are to be installed.

It doesn't even sound like we care what 300.6 says if we use a plastic wiring method


Greg Fretwell
#97902 04/15/06 06:59 AM
Joined: Jul 2002
Posts: 103
J
jes Offline
Member
I have used the Carlon clamps for years and they do a good job of raising the RNC just a little off the surface and at the same time allow it to slide with expansion and contraction better than an ordinary 2 hole strap. Would be my choice here. http://www.carlon.com/Brochures/2B10-Straps_Clamps.pdf

#97903 04/15/06 09:15 PM
Joined: Nov 2004
Posts: 53
H
Member
I have wired over 5 acres of production greenhouse. In Ohio where I did it, it was agricultural and not subject to inspection.
The inspector didn't even want to discuss methods.
I have seen RNC used and it turns into a terrible mess in a few years. The temperature swings make it expand and contract until it pops out of straps and busts fittings. If the greenhouse is unused and the heating and ventilating systems are shut down an 80 degree swing is easily possible.
Also the condensaion that occurs will fill any watertight raceway until the devices are swimming.
The best job I feel is done with EMT and set screw fitting to let the moisture out.
I have run EMT following the curved portions of the structures pretty sucessfully. Try using small bends at intervals and minis as straps.
Any tie wraps or T-stat/Low voltage wiring needs to be UV resistant or it will be toast in a couple years.
If it is a commercial operation the oxidation from the pesticides and fertilizers also will hasten the degradation.

Good Luck

#97904 04/15/06 09:54 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Wet location, aluminum MC?

added;
Drip loop so you enter the bottom of all boxes

[This message has been edited by gfretwell (edited 04-15-2006).]


Greg Fretwell
#97905 04/16/06 06:29 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
More great ideas and input. Thanks to everyone. Keep those cards nd letters coming!