supplemental grounding electrode #97487
02/22/06 07:55 PM
02/22/06 07:55 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
1)When a ufer ground is installed is a supplemental electrode required? (2) If one is required do I need 2 rods and do they have to be 6' min away from each other and the foundation?(as this is used for an electrode)(3)Can the #4 grounding electrode conductor be run through bored holes in the 2x10's to the panel?

2017 / 2014 NEC & Related Books and Study Guides
Re: supplemental grounding electrode #97488
02/22/06 08:31 PM
02/22/06 08:31 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I remember reading Mr. Ufer's reports on his grounding electrode. Under extremely adverse conditions, his method always performed far better than the 25 ohms code calls for. This was confirmed by Max Macomb, in his documentation that finally persuaded the code panels to accept the "Ufer ground."

If you're measuring over 25 ohms, I would suspect a problem with the measurement method.

But, there is no rule agains adding an electrode if you want to....but it needs to be six feet, or more, from the Ufer...which, in this case, means the entire slab. With a "Ufer," your slab is the electrode- not just that little copper wire!

While many measure the resistance of the ground by simply sticking their meter probe in the dirt....there has to be a reason for those pricey clamp-on meters, and other fancy equipment, used to measure grounding impedence.

Re: supplemental grounding electrode #97489
02/22/06 08:47 PM
02/22/06 08:47 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
Gserve:
In NEW construction, where a footing/foundation is being installed...it is mandatory that a Ufer be installed.

With a Ufer, no supplemental electrodes are required. (You may if you choose; they must be bonded together)

Yes, you may route the GEC thru wood framing.

As to the 'spacing'; IF you install, 6' spacing, like Reno stated above.

PS: You also have to 'bond' the water piping, jump the meter, bond the H&C at the wtr htr, etc.

John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,713
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,176 Are you busy
189,164 Re: Forum
178,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9527 MB (Peak: 1.0782 MB) Zlib enabled. Server Time: 2018-12-13 02:54:03 UTC