Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
1)When a ufer ground is installed is a supplemental electrode required? (2) If one is required do I need 2 rods and do they have to be 6' min away from each other and the foundation?(as this is used for an electrode)(3)Can the #4 grounding electrode conductor be run through bored holes in the 2x10's to the panel?

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
I remember reading Mr. Ufer's reports on his grounding electrode. Under extremely adverse conditions, his method always performed far better than the 25 ohms code calls for. This was confirmed by Max Macomb, in his documentation that finally persuaded the code panels to accept the "Ufer ground."

If you're measuring over 25 ohms, I would suspect a problem with the measurement method.

But, there is no rule agains adding an electrode if you want to....but it needs to be six feet, or more, from the Ufer...which, in this case, means the entire slab. With a "Ufer," your slab is the electrode- not just that little copper wire!

While many measure the resistance of the ground by simply sticking their meter probe in the dirt....there has to be a reason for those pricey clamp-on meters, and other fancy equipment, used to measure grounding impedence.

Joined: Apr 2002
Posts: 7,413
Likes: 10
Member
Gserve:
In NEW construction, where a footing/foundation is being installed...it is mandatory that a Ufer be installed.

With a Ufer, no supplemental electrodes are required. (You may if you choose; they must be bonded together)

Yes, you may route the GEC thru wood framing.

As to the 'spacing'; IF you install, 6' spacing, like Reno stated above.

PS: You also have to 'bond' the water piping, jump the meter, bond the H&C at the wtr htr, etc.

John