#97217 02/02/06 09:45 PM
Joined: Aug 2005
Posts: 251
T
Member
Does the ground wire to the 2 ground rods have to be continuous without breaks? Or can I have it go to the first ground rod secured with an acorn, then install another acorn to jump to the other rod?

So the ground wire is 2 pieces but attached with the acorns.


Shake n Bake
Work Gear for Electricians and the Trades

Workgear for Electricians

#97218 02/02/06 10:24 PM
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
No, it does not need to be an uninterrupetd run from the panel to both ground rods...only to the first one. This is the "GEC"
The wire between the two rods is considered a supplimental GEC.

#97219 02/02/06 11:00 PM
Joined: Aug 2005
Posts: 251
T
Member
thank you


Shake n Bake
#97220 02/03/06 06:15 PM
Joined: Aug 2003
Posts: 64
E
Member
I agree that the GEC ends at the first ground rod and does not need to continue unspliced from that point. However, conductors between ground rods or other electrodes in the grounding electrode system are more acurately called bonding jumpers. See 250.53(C)

#97221 02/03/06 09:33 PM
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Thanks, eprice....feel free to correct me!

#97222 02/07/06 11:48 AM
Joined: Aug 2003
Posts: 64
E
Member
Well, alright, I will, but its just that I so seldom find anything to disagree with in what you say [Linked Image]

#97223 02/08/06 06:09 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
You may also want to check with your power company, ours insists that it be one wire, continuous.


Few things are harder to put up with than the annoyance of a good example.
Work Gear for Electricians and the Trades

Workgear for Electricians

#97224 02/16/06 07:32 PM
Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
Tom,

Could you please send me a copy of that requirement for the continous run, is that Allegheny Power?

Thank you,

Les

[This message has been edited by LK (edited 02-16-2006).]