#96797 - 12/26/05 11:59 AM Leviton AFCI ad  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
There is a full page ad in the IAEI magazine from Leviton trying to get us to change the 2005 rule about AFCI devices. They want to be able to install them in the bedroom without the <6' and metal raceway rule.
Thoughts?


Greg Fretwell

2017 / 2014 NEC & Related Books and Study Guides

#96798 - 12/26/05 12:22 PM Re: Leviton AFCI ad  
Speedy Petey  Offline
Member
Joined: Aug 2003
Posts: 173
Upstate, NY
I think this is painfully obvious:

1) AFI's only come in breakers.
2) Leivton does not make breakers.
3) Leviton makes/sells wiring devices, etc.

ergo, ipso fatso:
4) Leviton wants to manufacturer and sell AFI devices.


I for one am all for it!!


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

#96799 - 12/26/05 01:31 PM Re: Leviton AFCI ad  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
When they started this AFCI stuff a while back, there were supposed to be devices avialable, as well as breakers. ('96 code?) That never happened, and it seems the whole thing got conveluted to the point where they (Manufacturers) were lobbying to have everything under the sun AFCI from the source at the CB, and ALL of them. (But not the main, or feeds, just every branch, maximizing special CB count.) 2002 NEC wants all outlets (Lighting etc.) AFCI'ed for "protection of the entire branch circuit." Not sure a "Device" could do that? Don't know about 2005 wording...

gfretwell, What "<6' and metal raceway rule" apply to AFCI's? (Guess I need to dig up that 2005 link...)

[This message has been edited by e57 (edited 12-26-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

#96800 - 12/26/05 01:54 PM Re: Leviton AFCI ad  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Just looked 2005 210.21 up, WOW it looks like CB manufacturers got to write thier own code there....

Sounds sneakingly familiar to a certain California towns rule on smoking 15' away from the sidewalk, i.e. between the double yellow line in the middle of the street. Allowed, but its not...


Mark Heller
"Well - I oughta....." -Jackie Gleason

#96801 - 12/26/05 09:30 PM Re: Leviton AFCI ad  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
I think Leviton should get their way on this one. It does make more sense to have the AFCI on the first outlet in the bedroom it controls. Perhaps they could even mount it outside in the hall if they want all wiring IN the bedroom to be protected but that is not true now. They only protect the "outlets". I can still run all the non-afci protected wire I want if it only serves outlets in other rooms.


Greg Fretwell

#96802 - 12/27/05 07:08 AM Re: Leviton AFCI ad  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I respectfully disagree with you on this one Greg and my reason is this: If the object is to protect the wiring in the building from arc fault it would make sense to me to protect as muchn of the circuit we can, which means keeping the device or breaker as close to the panel as possible. I think a lot of electricians are concerned about nuisance tripping and maybe they are worried about something that is probably not as big a problem as it was at one time. The benefit of arc fault protection fare outweigh any threat of nuisance tripping IMHO.


George Little

#96803 - 12/27/05 10:12 AM Re: Leviton AFCI ad  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
If you are worried about arcing wire inside the wall then why not say all wire passing through any bedroom connected wall on it's way to another room shall be AFCI protected?

That goes far beyond "is a switch an outlet?"

It has always been my understanding that the arc fault we are protecting against is the lamp cord pinched under the leg of the bed and buried in dust bunnies.
Isn't an arc in building wiring supposed to be inside a box?

If you are really saying a piece of Romex, between boxes, will burst into flames, maybe we should all be "chicago" with metal raceways.


Greg Fretwell

#96804 - 12/27/05 10:14 AM Re: Leviton AFCI ad  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
George, I cannot fault your desires...but, as I see it, the code should never create a situation where "best" is an enemy of "better."

We were told at the start of all this of the need to protect bedrooms from such things as loose plugs. The code gets edited, and Presto! we're now told we're supposed to be concerned about staples in the attic! Sounds like bait-and-switch to me!
Moreover, the code still fails to require- or even reccommend- separate circuits for the bedrooms; yet that is the practical effect of the AFCI requirement.

The biggest problem I have, though, is that the requirement assumes new construction, using a panel that will accept an AFCI. There are many places out there that still have fuses, or panels that are no longer made. There is no practical way to instal AFCI protection should you wish to uograde a circuit, or remodel a room.
This is unfortunate; I can add GFI protection to the oldest bathroom- but for a bedroom, I need to do a service change as well as replace all the old wiring. That is an unconscienable burden, and one that most impacts those least able to afford it.

Wouldn't everyone agree that protecting part of the circuit is better than protecting none of it?

As far as that 6-ft rule is concerned, I have yet to see any devices made available. This leaves me with the option of a sub-panel, which, ironically, would not require the use of pipe to feed it.

My final point: the cynic in me suspects that a device will cost a lot less than a panel-specific breaker. Until the panel makers agree to a uniform breaker pattern (that is interchangeable between brands), I will have to doubt their motives.


#96805 - 12/27/05 10:24 AM Re: Leviton AFCI ad  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
gfretwell,
Quote
It has always been my understanding that the arc fault we are protecting against is the lamp cord pinched under the leg of the bed and buried in dust bunnies.

That is what the manufacturers have been trying to tell us since the first AFCI proposal appeared in the ROP for the 96 code. In the 2005 code cycle they finally admitted that they really don't do that job...yet. They have promised that the combination type AFCIs that are required by the 2005 code with an effective date of 1/1/08 will actually do that. No one really knows yet, because there are no combination type AFCIs on the market at this time.
Don


Don(resqcapt19)

#96806 - 12/27/05 07:57 PM Re: Leviton AFCI ad  
HotLine1  Online Content


Member
Joined: Apr 2002
Posts: 6,878
Brick, NJ USA
Gentlemen:
I have to say that perhaps within the infinite wisdom of our State Legislators (NJ), they may have did the electrical trade a 'favor'. The arc fault requirements within the NEC are not adopted here.

At a seminar I attended a few months ago, I started a very heated debate about '....why isn't the lamp cord AFCI protected..????

The debate started with a 'statistic' on the quantity of electrical fires, and how many AFCI will prevent; the 'statistic' seemed to use a 'new' math, as the percentages and numbers did not add up. Needless to say, the final answer was....'maybe in '07 or '08'

John


John

Page 1 of 2 1 2

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,141
Joined: May 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 15 (0.003s) Memory: 0.8229 MB (Peak: 0.9994 MB) Zlib enabled. Server Time: 2017-12-12 16:10:21 UTC