ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#96666 12/16/05 09:03 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline OP
Member
So, I am pretty sure I know thge answer to this question, but looking for thought on this....

Here's the situation:
Water bond, +/or GEC (Supplimental) on the other side of building from Main. There's a slab being poured between each location, so I suggest conduit in slab for this, as it wont be possible to do latter due to steel in the way. PM orders 2 steel 90's and a bunch of PVC. (PVC is not allowed above slab in AHJ...) This is how many circuits are done.... So, here's where I need the fine opions of our members....

Quote
250.92(3)
Any metallic raceway or armor enclosing a grounding electrode conductor as specified in 250.64(B). Bonding shall apply at each end and to all intervening raceways, boxes, and enclosures between the service equipment and the grounding electrode.

My answer: It should be Non-metalic the whole way, (Not allowed here) or it should be metalic the whole way. As you could not bond the ends of the 90's or other conduit below slab. What do you think?


Mark Heller
"Well - I oughta....." -Jackie Gleason
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
e57:

if this is a common wiring method in your area, how is it bonded then?

Yes, I agree, all PVC, all RGC but you're between a rock & a hard place. I've seen guys around here just put a bonding bushing on the exposed 'ends'; Ive seen jobs with a 'bond jumper' (pipe clamp/clamps), etc.

One of our POCO's used to 'want' RGC at the riser on the pole, but it was always "wrong" no matter what bonding methods were used. Now, they want all PVC, all RGC.

John


John
Joined: May 2003
Posts: 2,876
E
e57 Offline OP
Member
No it is not a common method, normaly it would be RMC to EMT and bonded (W/hubs or bushings) at each end. Or no conduit at all...

Not EMT to RMC to PVC.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: May 2002
Posts: 1,716
R
Member
Mark, I agree. The "choke" or "girdling" effect will take place (although to what extent is debated) if the metalic sections of the raceway are not bonded to the GEC at both ends of these sections.


I remember an informative post or posts from Dereckbc on this subject once, maybe he or one of the other engineers will chime in.

The bottom line is it is a code requirement as you posted.

Roger

[This message has been edited by Roger (edited 12-16-2005).]

Joined: Dec 2005
Posts: 64
J
Member
can you cut a pvc 90 flush with the floor and run exposed gec above ground?

Joined: Jun 2004
Posts: 220
T
Member
I would say for other circuits, 250-86 ex#3 would allow you to not have to ground the 90's. But in the case of the GEC, It seems like a problem, although as to its magnitude I can't say. I agree with jwhite, if you have no issues with physical protection, why not go pvc to the level of the slab, then run GEC unportected from there?

Joined: Dec 2002
Posts: 308
E
Member
Probably running the GEC along the surface will be redtaged.

How about threaded metallic raceway all the way. (as you said mark)

On second note,
If you use threded metallic at both ends and pvc in buried section, why does the end of each metallic tail have to be bonded with a bonding bushing?

Edward


Thanks
Edward
Joined: Jun 2004
Posts: 220
T
Member
I was referencing 250-64B, and if the size and the circumstances allow, I don't see why you can't run it on the surface. As far as the bonding issue, take a look at 250-92 a(3). Now I am sure one of the smarter people on here can give you a presise answer, but as I understand it, the AC on a fault will try to flow in the conduit because of skin effect, and not in the GEC.

Joined: May 2003
Posts: 2,876
E
e57 Offline OP
Member
Running on surface not allowed due to 1) astetics 2)subject to damage in garage area.

PVC would need to exit in metalic at surface, or if cut off would need to be sealed as a building opening. Which I guess could be done...

Metalic the whole way is prefferable, easy, and only costs a few extra bucks.

Anyway, I guess I'm just sick of PM's who have no clue....


Mark Heller
"Well - I oughta....." -Jackie Gleason

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5