Grounding 12/2 and 14/2 cable in the same gang box #96546
12/06/05 08:20 AM
12/06/05 08:20 AM
D
damoski  Offline OP
Junior Member
Joined: Dec 2005
Posts: 2
Sterling, VA, USA
Prelude:
All ground conductors must be of sufficient size to trip the circuit breaker or fuse of the circuit that it protects, without overheating 15 amp circuit 15 amp wire, 20 amp circuit 20 amp wire. Refer to tables 250-94 and table 250-95, 1987 NEC (National Electrical Code).

Question:
I often combine two 14/2 cables from different circuits (15A fuses) in the same pigtail when wiring a three way switches. What are the implications of combining a 14/2 and 12/2 ground in the same pigtail?

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding 12/2 and 14/2 cable in the same gang box #96547
12/06/05 10:08 AM
12/06/05 10:08 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Check out 250.148 for the need to tie all equipment grounding conducors together. And, if the connector used for this tieing together is suitable for mixed sizes, I don't see a problem.

Just as a side note- How does the older issue of the code fit into this issue?

[This message has been edited by George Little (edited 12-06-2005).]


George Little
Re: Grounding 12/2 and 14/2 cable in the same gang box #96548
12/06/05 06:19 PM
12/06/05 06:19 PM
J
jwhite  Offline
Member
Joined: Dec 2005
Posts: 64
Trenton, NC, USA
you are supposed to combine them all in the same pigtail. and the tail to the device should be the rating of the circuit to that device.

and the code has had several cycles since your version

Re: Grounding 12/2 and 14/2 cable in the same gang box #96549
12/07/05 08:51 AM
12/07/05 08:51 AM
D
damoski  Offline OP
Junior Member
Joined: Dec 2005
Posts: 2
Sterling, VA, USA
Thanks very much for your response with regards to combining 14/2 and 12/2 ground in the same box. As for the reason I posted the code (granted it may be old: The ground conductor helps If there's an insulation or short to conduct the electricity away and possibly trip the breaker. In this case, a 14/2 is rated at 15A while a 12/2 is rated at 20A. In case of a short, the 14/2 doesn't seem to have the ca safely for a 20A circuit. May be I am reading too much into this, I need some coffee.

Thanks

Re: Grounding 12/2 and 14/2 cable in the same gang box #96550
12/07/05 01:01 PM
12/07/05 01:01 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
Within a reasonable length, #14 will safely trip a 20a breaker with a bolted fault. The theoretical resistance necessary is <6 ohms. That is about 500 feet. Since breakers vary in their trip curves and other things come into play you could probably say 100' is a safer number. Certainly any short jumper would not be a problem. You are still going to bump up against the code tho.


Greg Fretwell
Re: Grounding 12/2 and 14/2 cable in the same gang box #96551
12/07/05 06:17 PM
12/07/05 06:17 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
But when do you ever have a bolted fault?


Ryan Jackson,
Salt Lake City
Re: Grounding 12/2 and 14/2 cable in the same gang box #96552
12/07/05 07:27 PM
12/07/05 07:27 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
If it is an arcing fault, the minor difference in resistance between #12 and #14 is not going to make much difference.


Greg Fretwell
Re: Grounding 12/2 and 14/2 cable in the same gang box #96553
12/12/05 01:41 AM
12/12/05 01:41 AM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Plus, a #14 and a #12 paralleled have a lower combined resistance than either alone, so this only improves performance.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Grounding 12/2 and 14/2 cable in the same gang box #96554
12/17/05 07:55 PM
12/17/05 07:55 PM
E
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Does the nec require this. Both 14 and 12 egc to be tied together if they are in the same box.

i have always kept them separate.

Edwrad


Thanks
Edward
Re: Grounding 12/2 and 14/2 cable in the same gang box #96555
12/17/05 08:09 PM
12/17/05 08:09 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
as george little said above, 250-148 requires that where the circuit conductors are spliced, terminated on equipment within or supported by the box, the grounding conductor with the circuit must be spliced together.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,857 Are you busy
184,210 Re: Forum
173,451 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 14 (0.004s) Memory: 1.0102 MB (Peak: 1.1855 MB) Zlib enabled. Server Time: 2018-05-22 04:10:09 UTC