#96542 12/05/05 08:39 PM
Is there a code requirement for the distance that a incandescent type A-lamp would be required to maintain from combustible surfaces such as wood?
For instance, if a 60watt A-lamp, screwed into a keyless lampholder in a basement of a dwelling, was within an inch of a wooden rafter, this would seem to be a hazard.
410.5 gives me some guidance, but is there any other clear guideline that would specify distances from combustible material for type A-lamps?
shortcircuit
#96543 12/05/05 09:35 PM
Depends on the bulb used...do you have a thermocouple handy?
If I remember correctly, industry standards set 140 degrees F as the maximum temperature a fixture can cause on a "flamable" surface.
#96544 12/05/05 10:17 PM
e57 Offline
"within an inch of a wooden rafter, this would seem to be a hazard." - Yep....bulb to the side or below, I think it would be too close.
#96545 12/05/05 11:00 PM
410.5 Luminaires (Fixtures) Near Combustible Material.
Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).