#96431 11/28/05 11:01 PM
Joined: Sep 2004
Posts: 86
N
Member
I'm installing a spa disconnect for a hot tub that is strictly 230 volt operation so no need for a neutral. I see no reason to pull in a neutral conductor from the residential service panel for the pigtail on the GFCI 2 pole breaker and plan to terminate it on the ground bar with the separate equipment grounding conductor in the disconnect. Anybody see a violation here? Can't seem to find a concrete answer, even the inspector was scratching his head but has left it up to me to show it is ok. I'm up to the challenge but thought I would take a shortcut by asking if any of you fellas have already gone down this road.
Thanks
ron

Horizontal Ad
#96432 11/28/05 11:12 PM
Joined: Sep 2004
Posts: 174
B
Member
Didn't you get a wiring diagram with the disconnect? If I remember correctly you do not need to hook it up at all. I would just cap it. It isn't a ground so bonding it doesn't make much sense to me.


Jesus may have been a capenter,but God was an electrician.Genesis1:3
#96433 11/29/05 05:10 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Is this GFI breaker going to be the disconnect means?

It is a white wire, dont suppose you could tape it green? Just so some joker down the line doesn't put a neutral on it?

This is a good question. But why not just run the neutral? Capping is not good because it would have no refferance for ground, that is after all most of the purpose!


Mark Heller
"Well - I oughta....." -Jackie Gleason
#96434 11/29/05 09:52 AM
Joined: Jan 2004
Posts: 1,507
G
Member
GFCI breakers will monitor the current flow in all the conductors hooked up to them whether they are phase conductors or the white conductor. As soon as there is current flow exceeding 6ma. flowing someplace other than in those conductors connected to the breaker, the breaker will trip. Do not hook the white conductor to anything, unless it is needed by the load. No code reference other than maybe 110.3


George Little
#96435 11/29/05 09:57 AM
Joined: Jun 2001
Posts: 161
M
Member
To the best of my knowledge the circuit board in the GFCI won't work if there isn't a neutral, since the circuit runs on 120V. It is the same part that the single pole breakers use. (To test it out, disconnect the white pigtail and press the test button...) I don't remember any code provision that allows the use of a GEC for a neutral, even if it is for .001 watt... Besides, what about future accessories to the tub that do require 120V service?
IMHO, pull the white and there are no questions.

[This message has been edited by Mike Wescoatt (edited 11-29-2005).]


Mike Wescoatt
#96436 11/29/05 11:04 AM
Joined: Sep 2004
Posts: 86
N
Member
Thanks for the replies fellas
The problem is that this white pigtail is needed in the test mode of the breaker so just capping it wouldn't be practical. As 57 suggested, why not just run a neutral, is an easy way to be done with it but I am challenging my experiences and that of others to determine whether we really need to pull that neutral wire since the pigtail wouldn't be a current carrying conductor except possibly during a fault test. Although I will most likely just pull the neutral wire in to save on bickering time it would be nice to know, theory and code wise, whether it is necessary. The other point I was discussing with my apprentice this morning was the fact that the egc was terminated on the grounding bar in the spa disconnect so if I would terminate the "neutral" from the breaker at that point it could be said that now I've created a "service" point since the ground bar is bonded to the enclosure. Probably best to just pull the neutral in. Very fun discussion though. I will have to bring it up when together with others in the trade at the next convention.
Thanks again for all the replies.
Ron


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
366,229 Are you busy
289,088 Re: Forum
267,651 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5