#96346 - 11/20/05 08:15 AM Minimum size service  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Is there any section in the 2005 NEC that requires a minimum size electric service for dwelling or non-dwelling applications? I'm aware the local AHJ or power company may require a minimum size. My question has to do with the 2005 NEC only. Is it based on calculated load only?


2017 / 2014 NEC & Related Books and Study Guides

#96347 - 11/20/05 10:02 AM Re: Minimum size service  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Look at 230.42 and then go to 230.79 for further info as they reference in (B). There is no change from the '02.


George Little

#96348 - 11/20/05 12:45 PM Re: Minimum size service  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
The only (perceived) problem you might have with the PoCo is on the drop/lateral - they'll size to their estimation of demand, as opposed to your Code requirement calculated conductor size. Just remember, they operate under a different book than we do. [Linked Image]

A customer of mine wanted the ITE Pushmatic 8 spot panels on each side of his duplex upgraded to 200A modern panels (30 space GE) each when he added AC to the units. The AHJ allowed me (based on his load calc) to run 3/0 (maybe it was 2/0) up the riser, but the PoCo left the existing drop alone, stating that they didn't see enough of an increase in demand to warrant a change in conductors.

[This message has been edited by DougW (edited 11-20-2005).]


#96349 - 11/20/05 02:37 PM Re: Minimum size service  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thank you for the Code references. My question has been clearly answered.

[This message has been edited by Frank Cinker (edited 11-20-2005).]



Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.7609 MB (Peak: 0.8915 MB) Zlib enabled. Server Time: 2017-10-23 22:42:24 UTC