#96186 11/09/05 01:37 PM
Joined: May 2004
Posts: 116
S
Member
All -

What is the maximum height that a service panel (main cm panel)in a home can be?

I "seem" to remember (the second thing to go) that it is 6' with an exception that lets you go to 6.5'.

Am I having a "senior moment" or is it out there and I just can't find it?

A reference would certainly be great.

Thanks
Steve


Thanks
Steve
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96187 11/09/05 01:46 PM
Joined: Mar 2001
Posts: 345
T
Member
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.

Now the only question becomes is the highest breaker in the panel being used as a switch.
--
Tom Horne

[This message has been edited by tdhorne (edited 11-09-2005).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#96188 11/09/05 11:34 PM
Joined: Feb 2005
Posts: 693
L
Member
"Now the only question becomes is the highest breaker in the panel being used as a switch."

It is if it's the main service disconnect, meant to be manually operated.


Larry Fine
Fine Electric Co.
fineelectricco.com