#96088 - 11/02/05 10:27 PM 2 Ground Rods at Garage  
mvrandazzo  Offline
Member
Joined: May 2002
Posts: 110
Hi All.
When installing a sub panel at a garage using 4 6 awg's and driving a ground rod bonding it to the grounded conductor at the sub panel, can this ground rod be considered part of the grounding system at the house? Would it still be necessary to drive a second rod at the detached structure when there are 2 more at the house service location? For the longest time I have driven only 1 untill a recient inspection failed for not having a second at the garage. Am I missing something? I want to be sure I install them correctly.

Blessings,
Mark


2017 / 2014 NEC & Related Books and Study Guides

#96089 - 11/02/05 10:57 PM Re: 2 Ground Rods at Garage  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Mark- It appears that we may have a couple of issues with your question. My answer would be we need an electrode at the separate building based on 250.32 and this points us to Part III and 250.52 now an electrode consisting of a rod needs to be <25 ohms based on 250.56 and if not less than 25 ohms, most contractors will simply add another rod. Now for the second issue. You stated that you ran 4 number 6 AWG conductors to the garage leading me to think that you ran an equipment ground wire along with a "Grounded" conductor and 2 ungrounded conductors. If this the case, you would be "floating" the grounded conductor by leaving the bonding screw out of the neutral bus and your # 6 equipment grounding conductor along with your conductor going to your rod(s) will be terminated on a grounding bus that is fastened to the enclousure. (assume metal enclousure)


George Little

#96090 - 11/02/05 11:30 PM Re: 2 Ground Rods at Garage  
mvrandazzo  Offline
Member
Joined: May 2002
Posts: 110
Thanks George,
I understand. Driving a second rod is no big deal. Especially with a Hilti rod attachment. I misunderstood the code section.(Go figure). When driving grounding electrodes at a separate structure we DO NOT bond the neutral bar to the equipment ground when wunning 4 wire feeders. Then it may have been simpler to run 3 wire and bond at the subpanel.
Thanks

P.S. Good segment at the RECI Update. Somehow the whole course didn't seem as boring as it used to be. Maybe I'm just getting older.


#96091 - 11/03/05 12:30 PM Re: 2 Ground Rods at Garage  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
From a code perspective, I think you can make a good case that a second rod anywhere on the property that is bonded to the primary rod with an appropriate sized wire should be sufficient for the "augmenting" rod. This augmenting rod is required when you can't get 25 ohms from the primary rod. The only restriction i see in the code is that the rods must be at least 6 feet apart. The #6 EGC in your feeder would be sufficient bonding for a rod on any size of service or feeder.

I tried this once, and the inspector wouldn't buy it. I had enough other issues to challenge him on that I didn't press it, but I think the concept was just foreign to him.


Mark
Kent, WA

#96092 - 11/04/05 10:14 AM Re: 2 Ground Rods at Garage  
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
Quote
Originally posted by George Little
My answer would be we need an electrode at the separate building based on 250.32 and this points us to Part III and 250.52 now an electrode consisting of a rod needs to be <25 ohms based on 250.56 and if not less than 25 ohms, most contractors will simply add another rod.


Let’s take a closer look at 250.32

Quote
250.32(A) Grounding Electrode. Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with 250.50. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.


The only referral to a grounding electrode found in 250.32 is to 250.50. In 250.52 we are instructed to install one of the electrodes found in 250.52.

No where in either section 250.50 or 250.52 does it refer us to 250.56 for 25 ohms or less nor to 250.53 for the supplemental electrode for a metal water pipe.

I have submitted a proposal to have the reference to 250.50 removed and replaced with (Part III of 250).
As presently worded only one rod at a second building can be enforced.




[This message has been edited by jw electric (edited 11-04-2005).]


Mike

#96093 - 11/04/05 12:21 PM Re: 2 Ground Rods at Garage  
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
JW Electric,

I beg to differ, 250.56 is a stand alone code section. It says that all ground rods must meet the 25 ohm rule.

250.54 Supplementary Grounding Electrodes. has an exception to the 25 ohm rule, but these electrodes are not required by code.

250.32 does'nt have to refer you to 250.56 because it is general rule.

just MHO [Linked Image]

Chris


#96094 - 11/04/05 12:33 PM Re: 2 Ground Rods at Garage  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
JW Electric - Seems kind of nit-picky. With that reasoning, I think you could say you don't have to scrape any non conductive coatings off the rod (250.53A), don't have to drive it deep enough or straight in (250.53G), an aluminum GEC could be in the earth (250.64A), don't have to protect the GEC from damage (250.64B), ...

This isn't rational. To me, once you've been forced to install a ground electrode system as in 250.50, all of the sections of 250 Part III should be applicable. That being said, I think your code proposal does add clarity and reinforce what we all "know".

[This message has been edited by markp (edited 11-04-2005).]


Mark
Kent, WA

#96095 - 11/04/05 09:15 PM Re: 2 Ground Rods at Garage  
mvrandazzo  Offline
Member
Joined: May 2002
Posts: 110
Thanks All, Great responses. I, too think that it is unclear. Which is why I wonder why I was not cited from other municipalities before. Driving a second rod is no big deal. Hopefully it will be clarified in the next code cycle as JW has proposed.
Blessings,
Mark


#96096 - 11/04/05 11:34 PM Re: 2 Ground Rods at Garage  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
JW- I was using the '02 code because that's the code we are on in Michigan. I looked in the '05 at your reference and if I'm going to agree with you then I guess the code words at 250.54 are ridiculous. [Linked Image]


George Little


Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.8036 MB (Peak: 0.9680 MB) Zlib enabled. Server Time: 2017-10-21 06:36:39 UTC