310.15(a)(6) #95955
10/24/05 07:12 PM
10/24/05 07:12 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
When wiring a garage on residential property and feeding it from a separate feeder off of the main service panel mounted on a pole can I use this exception for the feeders or do they have to be per 310.15 table? In other words feeders to home as per 310.15(a)(6)and feeders to garage per 310.15(a)(6).

2017 / 2014 NEC & Related Books and Study Guides
Re: 310.15(a)(6) #95956
10/24/05 07:47 PM
10/24/05 07:47 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Read the article closely,

Quote
120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s). The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met.


Roger

Re: 310.15(a)(6) #95957
11/09/05 02:04 PM
11/09/05 02:04 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
IMUHO you can not use the residential service table for separate service conductors to a detached garage.

In the completely different case of the service conductors for a detached home that first runs to service equipment located in a detached garage you can only use the residential service cconductor sizing between the detached garage and the house but not between the service point and the service equipment that is located in a detached garage.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,506 Are you busy
186,194 Re: Forum
175,656 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9515 MB (Peak: 1.0754 MB) Zlib enabled. Server Time: 2018-08-14 08:26:19 UTC