Actuators for dampers #95813
10/07/05 12:51 PM
10/07/05 12:51 PM
B
bdh45  Offline OP
Junior Member
Joined: Jul 2005
Posts: 2
Are HVAC actuators for commerecial dampers considered motors? Do they have to meet the disconnect requirement in NEC 430.101? Any opinions would be appreciated.

2017 / 2014 NEC & Related Books and Study Guides
Re: Actuators for dampers #95814
10/07/05 03:16 PM
10/07/05 03:16 PM
R
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
I would tend to classify a damper actuator as an appliance.

422.31 (A): For permanently connected appliances rated at not over 300 VA or 1/8 HP, the branch-circuit overcurrent device shall be permitted to serve as the disconnecting means.

Most of the damper actuators that I have seen are pretty small.

Just MHO.

Chris

Re: Actuators for dampers #95815
10/08/05 02:11 AM
10/08/05 02:11 AM
S
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Most of the actuators I work on are 24v class 2. No need for disco.

Re: Actuators for dampers #95816
10/08/05 07:46 AM
10/08/05 07:46 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
Most of the actuators I work on are 24v class 2. No need for disco.


I do not see the fact that it is class 2 as the determining factor.

Disconnect switches are not only to keep us from getting shocks but also to keep us from getting caught in moving parts.

Many 24 volt damper motors can provide enough torque to amputate a finger.

I would like to believe that raider1 has the answer with 422.31 (A) but I am really not sure.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
dsk 3
Popular Topics(Views)
251,392 Are you busy
188,627 Re: Forum
178,328 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9593 MB (Peak: 1.0924 MB) Zlib enabled. Server Time: 2018-11-13 04:55:55 UTC