#95813 - 10/07/05 01:51 PM Actuators for dampers  
bdh45  Offline
Junior Member
Joined: Jul 2005
Posts: 2
Are HVAC actuators for commerecial dampers considered motors? Do they have to meet the disconnect requirement in NEC 430.101? Any opinions would be appreciated.


2017 / 2014 NEC & Related Books and Study Guides

#95814 - 10/07/05 04:16 PM Re: Actuators for dampers  
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
I would tend to classify a damper actuator as an appliance.

422.31 (A): For permanently connected appliances rated at not over 300 VA or 1/8 HP, the branch-circuit overcurrent device shall be permitted to serve as the disconnecting means.

Most of the damper actuators that I have seen are pretty small.

Just MHO.

Chris


#95815 - 10/08/05 03:11 AM Re: Actuators for dampers  
Sparks30  Offline
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
Most of the actuators I work on are 24v class 2. No need for disco.


#95816 - 10/08/05 08:46 AM Re: Actuators for dampers  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
Most of the actuators I work on are 24v class 2. No need for disco.


I do not see the fact that it is class 2 as the determining factor.

Disconnect switches are not only to keep us from getting shocks but also to keep us from getting caught in moving parts.

Many 24 volt damper motors can provide enough torque to amputate a finger.

I would like to believe that raider1 has the answer with 422.31 (A) but I am really not sure.


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7600 MB (Peak: 0.8901 MB) Zlib enabled. Server Time: 2017-10-24 06:02:13 UTC