#9573 05/11/02 08:58 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
The point is, there are reasons for both.

#9574 05/12/02 09:09 AM
Joined: Mar 2002
Posts: 360
T
Member
Thanks guys for the timely info. I have thirteen cast iron light poles to put up. The lights will be on three seperate controls. Can all the pole grounds be daisy chained together on one ground wire? Total amps of all thelights is approx. 15, and I will be pulling 10awg. Thanks
Trainwire

#9575 05/12/02 06:12 PM
Joined: Feb 2002
Posts: 36
3
Member
Menegt.....I don't know how your overhead layouts are going to be fed from, but if it's serving a private facility, it has been my experience that each one can be fused and depending on the voltage, I pull either a three or four conductor cable for each one, fed from an ac distribution box. That way each one gets its own EGC for the fixture itself. As far as the pole itself is concerned, I've always used 4/0 cadweld to the GEC whenever possible.....Burns

#9576 05/12/02 07:56 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
train--

Depends on voltage drop allowance and overcurrent device...99NEC250-122 could have a couple of applicable paragraphs.

#9577 05/16/02 02:31 AM
Joined: May 2002
Posts: 68
H
Member
your egc must be per code:

250-2. General Requirements for Grounding

(d) Performance of Fault Current Path. The fault current path shall be permanent and electrically continuous, shall be capable of safely carrying the maximum fault likely to be imposed on it, and shall have sufficiently low impedance to facilitate the operation of overcurrent devices under fault conditions.

The earth shall not be used as the sole equipment grounding conductor or fault current path.

250-122. Size of Equipment Grounding Conductors
(c) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.


Table 250-122. Minimum Size Equipment Grounding Conductors for Grounding Raceway and Equipment

Rating or Setting of Automatic Overcurrent Device in Circuit Ahead of Equipment, Conduit, etc., Not Exceeding (Amperes)

Size (AWG or kcmil)


Copper Aluminum or Copper-Clad Aluminum*
15 14 12
20 12 10
30 10 8
40 10 8
60 10 8
100 8 6
200 6 4
300 4 2
400 3 1
500 2 1/0
600 1 2/0
800 1/0 3/0
1000 2/0 4/0
1200 3/0 250
1600 4/0 350
2000 250 400
2500 350 600
3000 400 600
4000 500 800
5000 700 1200
6000 800 1200

remember this egc has to be sized for voltage drop so keep it the same size as your largest wire


Be Fair, Be Safe
Just don't be Fairly Safe
#9578 05/16/02 09:43 PM
Joined: Jan 2002
Posts: 34
M
menegt Offline OP
Member
Thanks 3dBurns.....