#95717 - 09/29/05 07:27 PM disconnecting means from building  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Is there a requirement in the code like in article 550 that addresses a maximum distance from the building to have a disconnect? I would like to have a pole mounted service and then feed the building which is 200' away there will be a main breaker in the panel closet to the point of entrance inside the building. Basically service on pole and feeder to building, service at building treated as sub-panel with isolated neutral,4 wire and also a GES. Or in other words how far can the service disconnecting means be from the building


2017 / 2014 NEC & Related Books and Study Guides

#95718 - 09/29/05 08:04 PM Re: disconnecting means from building  
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
Could this building fall under the scope of ARTICLE 547 Agricultural Buildings?
https://i3.photobucket.com/albums/y63/jwelectric/547.jpg


Mike

#95719 - 09/30/05 03:11 PM Re: disconnecting means from building  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
230.70(A)(1) requires the service disconnecting means to be either outside or inside the building nearest the point of entrance. And, 225.32 requires a disconnecting means for a remote building to be inside or outside, nearest the point of entrance of the conductors.
There are no numbers given, and it is up to the authority having jurisdiction to determine just how far away from the point of entrance constitutes "nearest".


Earl


Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7524 MB (Peak: 0.8758 MB) Zlib enabled. Server Time: 2017-10-23 02:31:45 UTC