disconnecting means from building #95717
09/29/05 07:27 PM
09/29/05 07:27 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
Is there a requirement in the code like in article 550 that addresses a maximum distance from the building to have a disconnect? I would like to have a pole mounted service and then feed the building which is 200' away there will be a main breaker in the panel closet to the point of entrance inside the building. Basically service on pole and feeder to building, service at building treated as sub-panel with isolated neutral,4 wire and also a GES. Or in other words how far can the service disconnecting means be from the building

2017 / 2014 NEC & Related Books and Study Guides
Re: disconnecting means from building #95718
09/29/05 08:04 PM
09/29/05 08:04 PM
J
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
Could this building fall under the scope of ARTICLE 547 Agricultural Buildings?
https://i3.photobucket.com/albums/y63/jwelectric/547.jpg


Mike
Re: disconnecting means from building #95719
09/30/05 03:11 PM
09/30/05 03:11 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
230.70(A)(1) requires the service disconnecting means to be either outside or inside the building nearest the point of entrance. And, 225.32 requires a disconnecting means for a remote building to be inside or outside, nearest the point of entrance of the conductors.
There are no numbers given, and it is up to the authority having jurisdiction to determine just how far away from the point of entrance constitutes "nearest".


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
BigB 4
Popular Topics(Views)
249,452 Are you busy
187,374 Re: Forum
176,710 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9515 MB (Peak: 1.0744 MB) Zlib enabled. Server Time: 2018-09-25 13:03:11 UTC