disconnecting means from building #95717
09/29/05 07:27 PM
09/29/05 07:27 PM
G
gserve  Offline OP
Member
Joined: Mar 2003
Posts: 92
Is there a requirement in the code like in article 550 that addresses a maximum distance from the building to have a disconnect? I would like to have a pole mounted service and then feed the building which is 200' away there will be a main breaker in the panel closet to the point of entrance inside the building. Basically service on pole and feeder to building, service at building treated as sub-panel with isolated neutral,4 wire and also a GES. Or in other words how far can the service disconnecting means be from the building

2017 / 2014 NEC & Related Books and Study Guides
Re: disconnecting means from building #95718
09/29/05 08:04 PM
09/29/05 08:04 PM
J
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
Could this building fall under the scope of ARTICLE 547 Agricultural Buildings?
https://i3.photobucket.com/albums/y63/jwelectric/547.jpg


Mike
Re: disconnecting means from building #95719
09/30/05 03:11 PM
09/30/05 03:11 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
230.70(A)(1) requires the service disconnecting means to be either outside or inside the building nearest the point of entrance. And, 225.32 requires a disconnecting means for a remote building to be inside or outside, nearest the point of entrance of the conductors.
There are no numbers given, and it is up to the authority having jurisdiction to determine just how far away from the point of entrance constitutes "nearest".


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013