#95535 09/19/05 05:54 AM
Joined: Sep 2005
Posts: 8
C
cruzer Offline OP
Junior Member
do you always ground the neutral on the prim. side of the gear.110-208 or 277-480

Horizontal Ad
#95536 09/19/05 09:24 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Cruzer- If you are talking about a (Grounded) Service the answer is located 250.24(A)(1) and you would be required to bond on the "primary" side of the switch gear. And I should also add the code reference 250.24(A)(4) which more directly answers the question on where you bond the "Grounded Conductor" to the equipment cabinet. See also 250.28.

[This message has been edited by George Little (edited 09-19-2005).]


George Little

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
365,347 Are you busy
288,196 Re: Forum
266,895 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5