by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 133 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2003
Posts: 259
J
Joey D Offline OP
Member
I got called on an inspection today for my boxes in a fire wall between two condo's. The inspector and myself didn't see the hr rating on the box. It was there I just missed it. He told me about these puddy pads that go over the box to make it comply.
I solved that issue but now there is an issue about boxes in the same bay. They need the pad and fire block insulation around them.
My point is should I be doing all this or should I just tell the contractor to do it as it's a building code?
Any projects from here on in will have a note about this though to cover myself.

Horizontal Ad
Joined: Apr 2002
Posts: 7,411
Likes: 7
Member
Joey:
As far as I know, the EC's around here do the putty pads/fire blanket thing. There's a 19 bldg apt complex going up, and the EC is doing the putty pad thing. There is supposed to be a 'rated box', but I have not seen it yet.

Careful layout avoids the multiple boxes in the same bay.....they need a minimum 24" spacing to the best of my knowledge.

John


John
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
We have to do it all the time. Putty pads, chalking. Recently found a good, (Darn pricey) foam that works well for multiple penetrations with conduit, made by Hilti.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Mar 2001
Posts: 2,056
R
Member
Allied Moulded Products Inc. makes a fiberglass box that, according to the literature reduces separation requirements from 24" to 3" without the use of putty pads.
http://www.alliedmoulded.com/Fire%20Rating%20Ad%207-2-04.pdf

[This message has been edited by Redsy (edited 09-14-2005).]

Joined: Aug 2003
Posts: 64
E
Member
With any non-metalic box, it's use in a fire rated wall depends on it's UL listing. When it comes to installing boxes in oposite sides of the same rated wall, the separation required varies greatly not only between manufacturers, but between different boxes by the same manufacturer. This information can be found by going to The UL web site and searching for UL categories QBWY and CEYY. I was able to find information for Allied boxes which can be spaced 3" apart as Redsy stated, but the wall must contain bat insulation.

I remember inspecting a motel where the electricain had used a variety of boxes by different manufactures. There were 6 or more different standards that needed to be applied throughout the building on a case by case basis depending on which box was used at a particular location. What a nightmare. My advise is, settle on a particular type of box that you will use throughout a project and stick with it. Find the UL information on the installation requirements for that box and use that information. Have it available for the inspector when he come.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
Popular Topics(Views)
347,089 Are you busy
272,200 Re: Forum
252,559 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5