Service Entrance Wires in Knoxville TN. #95399
09/12/05 06:42 PM
09/12/05 06:42 PM
B
Bomzin  Offline OP
Member
Joined: Mar 2004
Posts: 28
Utah
I was having a discussion with someone on a differant board and it was brought up that Aluminum wire could not be used to feed from service to panel. It was a not an electrician. Is this true and what is the reasoning behind it. Here in the state of Utah it is all that is used and don't see any problems with it when used correctly.

He also stated that for any home that is going to have central AC they had a 200 amp minimun on service requirments. Regardless of your load calculations.

Whats the scoop on this.
Thanks Bomzin

2017 / 2014 NEC & Related Books and Study Guides
Re: Service Entrance Wires in Knoxville TN. #95400
09/12/05 06:57 PM
09/12/05 06:57 PM
T
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
In my experience the issues of aluminum wiring and 200-amp minimum services are both local ammendments to the NEC by the AHJ, not Code issues.

Dave

Re: Service Entrance Wires in Knoxville TN. #95401
09/12/05 09:52 PM
09/12/05 09:52 PM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 734
Tucson, AZ USA
I have been told various things by mis informed people as well. The last one was that #14 wire is no longer allowed in new construction. This same person was "helping" a friend with a 200 amp upgrade, they were at Home Depot buying a piece of 2" EMT for the overhead riser. (Our POCO requires IMC). I just smiled at them and said good morning.

Re: Service Entrance Wires in Knoxville TN. #95402
09/12/05 10:38 PM
09/12/05 10:38 PM
J
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
My granddad was a wise man. One of the few times that he spoke he told me that it is sometimes better to keep thy mouth shut and thought a fool than to open it and let it be known.

This is a good example to a good time to keep his mouth shut.
[Linked Image]


Mike
Re: Service Entrance Wires in Knoxville TN. #95403
09/13/05 12:06 PM
09/13/05 12:06 PM
B
Bomzin  Offline OP
Member
Joined: Mar 2004
Posts: 28
Utah
Ok so it looks like Tiger thinks this is true with local codes writing it in and possibly 2 that think this is mis information.

I see it as possible, Tiger do you know this to be true or just taking a guess? Who is AHJ?

ty
Neil

Re: Service Entrance Wires in Knoxville TN. #95404
09/13/05 12:22 PM
09/13/05 12:22 PM
B
Bomzin  Offline OP
Member
Joined: Mar 2004
Posts: 28
Utah
Doh, Authority having juristiction , I knew that. Just put in an e-mail to the city inspector. Will post when I get info from the source.

Neil

Re: Service Entrance Wires in Knoxville TN. #95405
09/13/05 11:05 PM
09/13/05 11:05 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
I've seen homes with what was no doubt a greater current load in window A/C's than a central system would have provided.

Unless one is going all-electric, replacing several window units with a central system doesn't always need a service upgrade.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Service Entrance Wires in Knoxville TN. #95406
09/13/05 11:52 PM
09/13/05 11:52 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Larry You might be right in a practical sense because the window shaker load is hiding in the 3va per foot general lighting. Once you make it an HVAC load it has to be taken at nameplate value.


Greg Fretwell
Re: Service Entrance Wires in Knoxville TN. #95407
09/14/05 02:03 PM
09/14/05 02:03 PM
M
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
Really??? Aren't window shakers considered fastened-in-place equipment and therefore have to be tallied on a service calculation (that is assuming they were planned for when the electrician installed the service).


Mark
Kent, WA
Re: Service Entrance Wires in Knoxville TN. #95408
09/14/05 08:11 PM
09/14/05 08:11 PM
B
Bomzin  Offline OP
Member
Joined: Mar 2004
Posts: 28
Utah
Yes of course if the window unit were planned on you would have to consider it. Even after the fact it should be considerd.

The question still lies. If you do the math on a home in Knoxville and come up with only needing a 100 amp service or even a 125 but becuase you have electric range dryer and an AC unit you will be required to install a 200 amp service.

Also is aluminum wire ,SER, allowed or not from service to panel and if not what is the reasoning behind any of it .

Anyone from the city of Knoxville I mailed has yet to respond.

Just curious
Neil

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,540 Are you busy
188,098 Re: Forum
177,729 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 15 (0.004s) Memory: 1.0261 MB (Peak: 1.2005 MB) Zlib enabled. Server Time: 2018-10-21 12:42:25 UTC