#95181 - 09/03/05 08:55 PM Fill in blue boxes  
kyelectric  Offline
Member
Joined: Aug 2005
Posts: 64
Could anyone help me determine the fill on the blue plastic nail on box(4"x2"). Sometimes I have been in the situation where I needed to pull 4 12/2 w/G's in the blue box to connect to other circuits. I only count all the grounds 1 time, each individual conductor 1 time, the yoke (switch or receptacle) 2 times and each wire nut (clamp) 1 time. When I total this up it's 8 wires, 1 ground, 3 wire nuts, and 2 for the yoke. Total 14. I have seen this done many times in other jobs but it seems to be ok with most inspectors. Does anyone have some good input on this?


2017 / 2014 NEC & Related Books and Study Guides

#95182 - 09/03/05 09:08 PM Re: Fill in blue boxes  
Ralpha494  Offline
Member
Joined: May 2004
Posts: 73
Pewaukee,WI,USA
IMHO the wire nuts aren't clamps so you don't count them. If you don't put in a device (just a blank cover) you get 2 more back. It should end up being 8 wires plus 1 ground for a total of 9 (or 11 with a device).


#95183 - 09/03/05 09:31 PM Re: Fill in blue boxes  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
The biggest single gang carlon nailup I have seen is the 3¼ deep and that is 22 cu/in, That is still too small for 11 #12s. (9 wires and the device)

2¼ x 11 = 24.75


Greg Fretwell

#95184 - 09/05/05 01:09 AM Re: Fill in blue boxes  
georgestolz  Offline
Member
Joined: Jun 2005
Posts: 91
Fort Collins, CO, US
Quote
Sometimes I have been in the situation where I needed to pull 4 12/2 w/G's in the blue box to connect to other circuits. I only count all the grounds 1 time, each individual conductor 1 time, the yoke (switch or receptacle) 2 times and each wire nut (clamp) 1 time.

As mentioned above, wire nuts are not clamps. See 314.16.

Clamps attach the cable to the box, not conductors together. [Linked Image]

The easiest way to keep these things straight when first getting them straight, IMO, is to go down the list one by one:

So 4 12-2's with 1 device are
8 insulated conductors (314.16(B)(1))
0 Clamps (314.16(B)(2))
0 Support Fittings (314.16(B)(3))
2 counts for 1 device (314.16(B)(4))
1 count for all EGC's (314.16(B)(5))


Is 11 conductors x 2.25 = 24.75 cu.in.

That's way over for a single gang, even Carlon. (gfret, box fill is something best understood when the same math is done four different ways. [Linked Image] )


-George

#95185 - 09/05/05 08:26 AM Re: Fill in blue boxes  
Mvannevel  Offline
Member
Joined: Mar 2003
Posts: 29
Hesperia, Michigan, USA
And for those of us whose arithmeticer's don't work so good, Carlon boxes have the maximum number of each size conductor marked in the back of the box. Takes the guesswork out of it if you're not handy with the math.


#95186 - 09/05/05 08:40 AM Re: Fill in blue boxes  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Nice job Just George


You got sucked in didn't you?

Don't blame me. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#95187 - 09/05/05 10:11 AM Re: Fill in blue boxes  
georgestolz  Offline
Member
Joined: Jun 2005
Posts: 91
Fort Collins, CO, US
Well, I ran out of stuff to do at my normal haunt. [Linked Image]

Everybody's enjoying their three-day weekend. Did you see me hanging off the rock?

-George S.


-George


Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7861 MB (Peak: 0.9389 MB) Zlib enabled. Server Time: 2017-08-22 03:48:20 UTC