#94893 08/17/05 09:22 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Has anyone on this forum had any experience with the floor heating system manufacturered by "Heatizon"? Since seeing it on a job installed in a bathroom, I am concerned about the requirement for GFCI protection. The voltage is about 36v. and the primary voltage is 240v. Look at 224.44(G).


George Little
Work Gear for Electricians and the Trades

Workgear for Electricians

#94894 08/18/05 03:28 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I have heard some are adding built-in GFI protection, not sure about this one.... Haven't seen it yet.

And yep, if in a situation described by the code you refferance, requires protection, one way or the other.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#94895 08/18/05 10:48 PM
Joined: Jul 2004
Posts: 10,037
Likes: 37
G
Member
I left this one alone because we don't do a lot of heated floor in S. Florida.

Reading 424.44(G) I don't see any relief from the GFCI rule because it is 36v.

I would certainly defer to an AHJ who had actually seen one tho.


Greg Fretwell
#94896 08/18/05 11:01 PM
Joined: Apr 2002
Posts: 558
C
Member
I don’t know anything about the Heatizon system but the digital thermostats included with all the floor systems I have worked with have integral GFCI protection.


Curt Swartz