Panel identification #94867
08/16/05 07:04 PM
08/16/05 07:04 PM
B
boggerbutt2454  Offline OP
Member
Joined: Feb 2005
Posts: 44
Concord NC USA
I had inspector tell me he wants a label on the front of the panel for 120/208 that say's
A phase black
B phase red
C phase blue
for 277/480
A phase brown
B phase orange
C phase yellow
He said this is a new code but the reference he gave didn't state this.

Is this something new? I always thought the color code was sort of a rule of thumb that all electricians knew the color code although I have seen some that use black, red, blue for everything.

[This message has been edited by boggerbutt2454 (edited 08-16-2005).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Panel identification #94868
08/16/05 07:33 PM
08/16/05 07:33 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Except for white, green, and gray, coloring is purely arbitrary. If anyone knows differently, please advise.

[This message has been edited by Larry Fine (edited 08-16-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Panel identification #94869
08/16/05 07:44 PM
08/16/05 07:44 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The colors you choose are up to you, the NEC would allow purple, pink and brown for 480 volt.

However in some instances the NEC does require that the colors you choose to be listed at the panel.

In the 2002 NEC it applied only to multiwire branch circuits.

Quote
210.4 Multiwire Branch Circuits.(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.


Now in the 2005 it applies to all circuits in some buildings.

Look at 2005 - 210.5(C)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Panel identification #94870
08/16/05 09:54 PM
08/16/05 09:54 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
But in the 2005 code there is no requirement that each phase have a different color...only each system.
Don


Don(resqcapt19)
Re: Panel identification #94871
08/16/05 11:46 PM
08/16/05 11:46 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
You do still have this one;
110.15 High-Leg Marking.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded to supply lighting and similar loads, the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present.


Greg Fretwell
Re: Panel identification #94872
08/16/05 11:53 PM
08/16/05 11:53 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Absolutely right, GFret. My bad.


Larry Fine
Fine Electric Co.
fineelectricco.com
Re: Panel identification #94873
08/17/05 01:43 AM
08/17/05 01:43 AM
R
Rhino  Offline
Member
Joined: Jun 2004
Posts: 24
San Diego,California,USA
A lot of the fine points of our trade and codes hilighted here!
Really kind of a treat!
Thanks to all that contribute

Re: Panel identification #94874
08/17/05 06:23 PM
08/17/05 06:23 PM
B
boggerbutt2454  Offline OP
Member
Joined: Feb 2005
Posts: 44
Concord NC USA
Thanks iwire, I must have read over 210.4 a couple of times and missed it each time. Like they say if it had been a snake it would have bit me.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,097 Are you busy
185,543 Re: Forum
174,841 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9938 MB (Peak: 1.1532 MB) Zlib enabled. Server Time: 2018-07-17 05:37:51 UTC